โDec-22-2013 07:16 PM
โDec-23-2013 01:45 PM
Dutch_12078 wrote:Bumpyroad wrote:Bob Landry wrote:
I'm simply stating that is is OK to have one side of DPDT breaker unused or it can be used for the neutral leg.
but the "unused" half of the breaker would be connected internally to the other "hot" side of the box???
bumpy
There is no internal electrical connection between the two legs of the breaker. If one side overloads, both sides will trip, but that's just a mechanical connection. One side not being connected will not effect the breaker operation for the connected side.
โDec-23-2013 01:41 PM
Bumpyroad wrote:Bob Landry wrote:
I'm simply stating that is is OK to have one side of DPDT breaker unused or it can be used for the neutral leg.
but the "unused" half of the breaker would be connected internally to the other "hot" side of the box???
bumpy
โDec-23-2013 01:05 PM
โDec-23-2013 10:36 AM
Bob Landry wrote:
I'm simply stating that is is OK to have one side of DPDT breaker unused or it can be used for the neutral leg.
โDec-23-2013 09:23 AM
Bob Landry wrote:kbotley wrote:
I recently converted from a dual hot water tank setup in my house to a single tank resulting in an unused 30amp double pole breaker. I would like to use this breaker and the 10ga wire to power a TTL-30 outlet for my RV when it's in the driveway. Since the double pole is 240V through 2 conductors and I only need 120v is it acceptable to terminate the red conductor and just use the black (hot) white (neutral) and bare (ground) on the double pole breaker?
Thanks
Ground does not go through the breaker, It goes to a separate bus to which all of the safety grounds going into the box are attached. It's OK to use just one side of a DP breaker as an over load on the hot leg will cause both of them to trip. I haven't seen it done in residential, but in marine shore power systems we have both hot and neutral going through a DPDT breaker because neutral is considered to be a current carrying leg and both must be broken. Before an armchair electrician jumps on my last statement, our electrical standards are set and regulated by ABYC and the USCG and do not run in lock step with the NEC. I'm simply stating that is is OK to have one side of DPDT breaker unused or it can be used for the neutral leg.
โDec-23-2013 09:02 AM
kbotley wrote:
I recently converted from a dual hot water tank setup in my house to a single tank resulting in an unused 30amp double pole breaker. I would like to use this breaker and the 10ga wire to power a TTL-30 outlet for my RV when it's in the driveway. Since the double pole is 240V through 2 conductors and I only need 120v is it acceptable to terminate the red conductor and just use the black (hot) white (neutral) and bare (ground) on the double pole breaker?
Thanks
โDec-23-2013 07:40 AM
โDec-23-2013 06:34 AM
โDec-23-2013 06:07 AM
โDec-23-2013 05:57 AM
Bumpyroad wrote:
$5??? when was the last time you bought a breaker 1945?
bumpy
โDec-23-2013 05:53 AM
RJsfishin wrote:
Some of the old 240v breakers were 2 single pole pinned together. If the above is true, just un pin it.
โDec-23-2013 05:46 AM
Hank MI wrote:RJsfishin wrote:Bumpyroad wrote:
so what people are saying is that with a double pole breaker, both sides must exceed load limit to trip? is that correct?
bumpy
I would have exactly the same question, but when I think of how 240 doesn't use or need a common, its probably true.
Not true in all cases. A straight 240v load, such as a well pump, won't need a common but not all 240v loads are the same. An electric range may use 240v for heating elements and 110v for lichts and controls. That requires a common because it's an unbalanced load.
Because 240v loads are often unbalanced an overload on one leg will trip a double pole breaker. But I would spend the $5 and replace it with a single pole
โDec-23-2013 04:29 AM
RJsfishin wrote:Bumpyroad wrote:
so what people are saying is that with a double pole breaker, both sides must exceed load limit to trip? is that correct?
bumpy
I would have exactly the same question, but when I think of how 240 doesn't use or need a common, its probably true.