Dave H M wrote:wa8yxm wrote:
Code calls for a single ground basically at the meter (The first breaker box past the meter is where it goes) in the garage you shoudl have a SUB box. the ground bus in this is NOT bonded to neutral but is connected to the master ground back at the master box.. And that is how it should be.
And there is always a way to run a ground rod. even if it's solid concrete you need to drill through.
But since the proper way is to ground back to the main breaker box ground.. and that wire should already be there.. Don't worry about it.
Since i am curious about all the electrical beliefs, rumors and urban legend, I read through All the posts.
This is the one that hit the nail on the head. Way it is done here. :C
โAug-18-2015 05:45 AM
wa8yxm wrote:
Code calls for a single ground basically at the meter (The first breaker box past the meter is where it goes) in the garage you shoudl have a SUB box. the ground bus in this is NOT bonded to neutral but is connected to the master ground back at the master box.. And that is how it should be.
And there is always a way to run a ground rod. even if it's solid concrete you need to drill through.
But since the proper way is to ground back to the main breaker box ground.. and that wire should already be there.. Don't worry about it.
โAug-17-2015 10:02 PM
โAug-17-2015 10:06 AM
โAug-17-2015 09:09 AM
โAug-17-2015 08:06 AM
โAug-17-2015 07:52 AM
โAug-17-2015 07:46 AM
westend wrote:
I'd suggest to break out the hammer drill, drill a hole close to the load center you installed, and install a ground rod. Yeah, drilling through old barn floors and feed lot slabs can be tedious but a ground rod with short path to the load center is an ideal situation. If any device does short to ground, the length of the ground wire will be energized. A jacketed wire won't be too much of an issue but if the ground wire is bare copper, any flammable stuff on it may ignite.
It sounds like there was little thought to bringing any new service up to a reasonable state by the owner or past occupants. Now would be the time to get it as close to good as possible.
โAug-17-2015 07:16 AM
โAug-17-2015 06:50 AM
โAug-17-2015 05:21 AM
Goostoff wrote:
Unfortunately you are trying to make it a lot easier than it is.
โAug-16-2015 06:25 PM
Vulcan Rider wrote:KD4UPL wrote:
To meet code you need to drive a rod at the garage and ground the panel.
LIke a lot of other problems posted here......you are making this a lot harder than it really IS.
The 3 existing wires have to get into the building through some kind of a hole.....right ?? Drive a ground rod OUTSIDE near that hole and run the ground wire into the building through the same hole that the other wires already use. If necessary, chip out a little mortar or sealant to make room.
If you trace the feed wires back to a pole, there should be a ground rod at that pole, connected up to the transformer. That's where the real ground/neutral makes it's connection.