Yes you are right, leaving it at 78, and it probably would not freeze up, because the coil temp will stay above 45F.
Leaving the fan in 'on' would have also thawed out any frost on the coil during any compressor 'off' time. However if the thermostat was set cold enough, and there was no off time, then the coil can still freeze.
Check your air temp output. You might have a freon leak, and it is best to change the A/C while the unit is new as possible. Then you will still have 5 more months to test the replacement unit, under warranty if required. Don't think they only have a 6 month lifespan, my 1997 unit is the factory one, so they do last a long time.
So if air in is 85F, then air out should be between 18 and 22F cooler. So 63 - 68F would be acceptable. I am suspecting that your air is not coming out very cold, and as a result the compressor rarely shuts off, and that caused it to freeze. (because the compressor ran so many hours without freezing you out).
Lets say that the rear A/C is getting the air cooler by 22F, and the front one only cools the air by 12F. This means that the back one is working great, and the front one will take more than 10 hours to cool that area, good thing you have the second one! And with less than 15F temp cooling, they need to replace the front one under warranty, unless they can find the leak and repair it.
I did repair a leaking rooftop RV A/C once for a friend. It took me about 4 hours, and the leak was right there, easy to repair and install the fittings, and then evacuate, and recharge it. If my work had billed for my time, the estimate would have been something like $725. That is $150 an hour X4 and $62 in materials X2.
Good luck!
Fred.