Amps Size for Finishing Stage Charger
Scenario is you are on shore power and your regular charger (limited to 14.x volts) gets the batts to about 90% SOC, then you apply your special finish stage charger that can do 15.x volts but is limited in amps.
(This might apply to a solar controller too but generally you would not do this on generator due to the long run time when charging at over 90% SOC.)
Using the marker of 5 amps per 110AH of battery for acceptance rate at 14.4 volts at 90% SOC, the question is what would be the acceptance rate if you cranked the voltage to 15.5 at that point? That would tell you the highest amps size of finish charger it would be worth getting---knowing how many AH of bank you have.
Ok I ran a test on my 458AH bank using my variable voltage charger where amps got down to 21a as my marker for being at 90% and voltage was 14.4 (458/110 x 5 = 20.8)
I then jacked up the voltage on the charger to 15.5. Battery acceptance jumped to 34.3 and battery voltage to 15.1. Within two minutes, amps were down to 31ish and tapering with voltage 15.2ish.
So very roughly, it would seem sensible to have the 15.5v finish charger be able to do about 32a for four batts so call it "30a" for charger size. and so that would be 15a for a pair of batts.
No point in going larger in amps when the batts won't accept any more amps than that. Amps were tapering so you could say to go even lower in max amps for the little time it would stay at 30 or 15. For the money and time, optimum might even be say, 20 and 10.
Anyway that is sort of what you are looking at in that scenario, it seems.
(This might apply to a solar controller too but generally you would not do this on generator due to the long run time when charging at over 90% SOC.)
Using the marker of 5 amps per 110AH of battery for acceptance rate at 14.4 volts at 90% SOC, the question is what would be the acceptance rate if you cranked the voltage to 15.5 at that point? That would tell you the highest amps size of finish charger it would be worth getting---knowing how many AH of bank you have.
Ok I ran a test on my 458AH bank using my variable voltage charger where amps got down to 21a as my marker for being at 90% and voltage was 14.4 (458/110 x 5 = 20.8)
I then jacked up the voltage on the charger to 15.5. Battery acceptance jumped to 34.3 and battery voltage to 15.1. Within two minutes, amps were down to 31ish and tapering with voltage 15.2ish.
So very roughly, it would seem sensible to have the 15.5v finish charger be able to do about 32a for four batts so call it "30a" for charger size. and so that would be 15a for a pair of batts.
No point in going larger in amps when the batts won't accept any more amps than that. Amps were tapering so you could say to go even lower in max amps for the little time it would stay at 30 or 15. For the money and time, optimum might even be say, 20 and 10.
Anyway that is sort of what you are looking at in that scenario, it seems.