BFL13 wrote:Baja Man wrote:BFL13 wrote:
OP is asking about plugging into gens, but the two receptacles are in the paraLink.
The neutral-grounding plugs I am referring to are plugged into the inverters 120V receptacle
I have seen the bonded 15a adapters used for that and you would have one on the shore power cord plug. You say you will be using the parallel kit, so you will be plugging into one of the two 30a paraLink receptacles depending on your plug type, not into one of the gens.
Do you intend to have a 30a adapter modified to be bonded? Very confusing.
He’s planning to plug the RV into the paraLink kit but the bonding plug into one of the 120V receptacles on one of the generators.
The answer is it will work fine so long as the ground wire (I.e. the screw loop terminal) from the paraLink is connected to the ground lug on the generator with the bonding plug.
All bonding does is connect the green ground wire to the neutral. Once all neutrals are connected to each other and all grounds are connected to each other bonding can be done on either generator or at the unused the paraLink receptacle.