jbrack
May 21, 2019Explorer
Atwood Furnace
I'm a little frustrated with my Atwood furnace. I have a 2018 5th wheel that I bought at the RV show in Sacramento. I hit the road to Arizona and almost immediately had trouble with the furnace. Fo...
jbrack wrote:starcraft69 wrote:Old-Biscuit wrote:
Burner cycling on then off/back on/off is called 'limiting' which is when the airflow has been restricted and heat exchanger high temp limit switch is opening (too hot) then fan continues to run so temp drops...high temp limit switch closes and burner lights back off
You have something obstructing/blocking either the furnace discharge air flow OR the return air to furnace
Could be closed/blocked register, could be crushed ductwork, could be how/where stuff is stored
Fan runs cause high temp limit switch opened.burner keeps firing back off cause thermostat temp set point has not been met....high temp limit switch controlling burner shutting down/relighting
Listen to this man! This is the correct answer.
This makes the most sense to me...and has been suggested to me before but none of the mechanics who have looked at the furnace have investigated this. None of my inside vent are blocked or restricted. I can see most of the ductwork from inside the belly but cant see the duct that feeds the one floor vent in the extreme rear of the coach. My next question is...if I continue to operate the furnace in this on/off fluctuating mode, will it cause any damage?