Hi,
I think I've reached the end of my Googling skills and would really appreciate your guidance.
I am wiring my 6x12 enclosed trailer for a rooftop (13.5k) AC & four duplex outlets that will be used for basic purposes such as charging phones & computers and running some LED puck lights. Currently I don't have any plans for a DC environment.
I have a 30 Amp inlet that will be connected mostly to a pair of EU2000i generators and sometimes to a 50 or 30 Amp RV park outlet.
My issue relates to finding the best (safest) option for a breaker panel.
I am planning to use a 20A breaker for the AC and a single 15A breaker for the outlets.
If I use a main lug panel (no main breaker) those two breakers could total 35A and I am concerned that there would be a potential hazard since I'll be using a 30A extension cord as well as 10/2 wire from the inlet to the trailer's breaker.
I can't seem to find a 30A main breaker panel and most seem to be 100A or higher... So if I was to install a 100A main breaker I would still have the same issue of potentially sending 35A across my 30A extension cord.
Another alternative I've considered is using a 30A breaker on a main lug panel and then back-feeding it in order to create a quasi-main breaker, though this seems to be a controversial method on the internet, and if it's dangerous in any way I'm not interested.
Do you know if there is a 30A main breaker available on the market? Is it possibly ok to forgo a main breaker and just use the 20A & 15A breakers? Am I over-thinking this?
Thanks in advance,
Mark
I think I've reached the end of my Googling skills and would really appreciate your guidance.
I am wiring my 6x12 enclosed trailer for a rooftop (13.5k) AC & four duplex outlets that will be used for basic purposes such as charging phones & computers and running some LED puck lights. Currently I don't have any plans for a DC environment.
I have a 30 Amp inlet that will be connected mostly to a pair of EU2000i generators and sometimes to a 50 or 30 Amp RV park outlet.
My issue relates to finding the best (safest) option for a breaker panel.
I am planning to use a 20A breaker for the AC and a single 15A breaker for the outlets.
If I use a main lug panel (no main breaker) those two breakers could total 35A and I am concerned that there would be a potential hazard since I'll be using a 30A extension cord as well as 10/2 wire from the inlet to the trailer's breaker.
I can't seem to find a 30A main breaker panel and most seem to be 100A or higher... So if I was to install a 100A main breaker I would still have the same issue of potentially sending 35A across my 30A extension cord.
Another alternative I've considered is using a 30A breaker on a main lug panel and then back-feeding it in order to create a quasi-main breaker, though this seems to be a controversial method on the internet, and if it's dangerous in any way I'm not interested.
Do you know if there is a 30A main breaker available on the market? Is it possibly ok to forgo a main breaker and just use the 20A & 15A breakers? Am I over-thinking this?
Thanks in advance,
Mark