j-d wrote:
When you cleaned, were you able to get to both sides of the Evaporator Coil, and clean the Drain Pan (and its drain holes)?
Have you tried running it on HIGH Fan, or only Low?
Gotta say, I don't like the 69* but I want to add that a temp gun isn't as good for measuring air temp as a thermometer is.
Do you have a Clamp-On Ammeter? Your compressor should be marked "RLA" for Running Load Amps. If you measure the Amps at the main connection to the A/C, then find the RLA for the Fan and add that to the Compressor's RLA. If the actual Amp Draw is less than that (or grossly more than that) it's likely there's compressor trouble or a refrigerant leak.
Do these things leak? Sure, but not all that often, and Coleman seems to be one of the tighter ones. I thought I had to replace the 1983 Coleman Mach 13500 till I cleaned it. Thing wasn't cooling, and the Evap was freezing over. After cleaning, it cooled very well again, and ran well till we sold the coach in 2008. It was then, that I picked up the "run fan on High" tip and it's really helped.
Our present coach has Coleman Mach 15000, still running since 2002 (some years full time) with only cleaning and a new blower motor.
Both the 13500 and the 15000 units are non-ducted. I cut intake filters from "30-day" home A/C filters and change them often. One 20x20 filter gives me two sets for the RV.
โJun-19-2017 08:57 AM
TenOC wrote:
...coil freezing is caused by low Freon... On my home A/C there is a thermostat located at the coils...
โJun-19-2017 06:32 AM