GENERAC GENERATOR ISSUE

I have a Generac generator in my 1995 Damon Intruder (GN-480 Q-55).

If I prime it on the gennie it starts and runs fine for about 1-2 minutes then quits, however if I keep prime switch down or press it for 3 secs every 1-2 minutes it runs fine.
Gennie is providing power as fridge and lights go on after a few seconds and I switch breakers on.

I replaced the fuel pump and filter (no change in symptoms)
Gas tank is full.
Same symptoms if I disconnect the low oil & temp sensors.
I replaced the Prime rocker switch as it was cracked (the one I used has three positions and will stay ON unless switch to OFF). Thinking back I attached the 3 wires in what I thought was correct order but now I'm wondering if I could possibly have connected the 3 wires incorrectly.

Should the fuel pump run continuously (I presume YES)? Should the control board take over the fuel pump once prime switch is released.

Is it harmful to keep the Prime switch on?

I was going to clean carb but someone suggested that is unlikely given symptoms, however I am willing to try anything as I am reluctant to delve into control board issues at this point.

Thanks for any help.