Generator/AC/converter questions
My travel companion and myself are going to buy a generator for use on an extended trip this summer. It will definitely be an inverter type, and we are looking at the Champion models. We just need to figure out which one we need.
So help me figure out some things here:
1) A generator with 3100 watts peak output at 120V can produce 3100/120 = 25.8 amps. Is this correct?
2) The Advent 13500 BTU AC info we have says "12.4 amps is the load associated with the AC." So 12.4 amps X 120V = 1488 W. Is this the starting amps or running load?
3) The converter is a WFCO 8955. According to the WFCO website, the power input is 950 W. Is this what it will pull off a generator?
4) So if we plug into the generator and run both the converter and the AC, power consumption would be 2438 W. Is this correct?
5) Assuming a 10% "efficiency" loss, 2438 W/0.90 = 2700 W that would need to be supplied by the generator. Is that a reasonable assumption?
6) Is there any way to turn off the converter draw if the AC is running?
We are looking at the 3100 watt dual fuel Champion generator at Costco. According to Champion, it has:
gas--3100 peak, 2800 run
propane--2800 peak, 2520 run
Trying to decide if the propane would be adequate. Looks like it would be IF the 12.4 amps is the starting load from the AC unit. Otherwise, not.
If not, we will go with the single fuel 3400 peak version from Tractor Supply (best price we've found.)
Any input appreciated!
So help me figure out some things here:
1) A generator with 3100 watts peak output at 120V can produce 3100/120 = 25.8 amps. Is this correct?
2) The Advent 13500 BTU AC info we have says "12.4 amps is the load associated with the AC." So 12.4 amps X 120V = 1488 W. Is this the starting amps or running load?
3) The converter is a WFCO 8955. According to the WFCO website, the power input is 950 W. Is this what it will pull off a generator?
4) So if we plug into the generator and run both the converter and the AC, power consumption would be 2438 W. Is this correct?
5) Assuming a 10% "efficiency" loss, 2438 W/0.90 = 2700 W that would need to be supplied by the generator. Is that a reasonable assumption?
6) Is there any way to turn off the converter draw if the AC is running?
We are looking at the 3100 watt dual fuel Champion generator at Costco. According to Champion, it has:
gas--3100 peak, 2800 run
propane--2800 peak, 2520 run
Trying to decide if the propane would be adequate. Looks like it would be IF the 12.4 amps is the starting load from the AC unit. Otherwise, not.
If not, we will go with the single fuel 3400 peak version from Tractor Supply (best price we've found.)
Any input appreciated!