LouLawrence wrote:
50 amp service equals 12,000 watts (2 legs of 50 amp = 100 amps @ 120V) x 2 vehicles equals 24,000 watts. Add in the 30 amp coach at 3600 watts and you need 27,600 watts to properly service all 3 RV's. You would need a substantial generator to supply the power to all 3 and that would be done by feeding the service from this 30,000+ watt generator to a sub-panel from which you could run 3 proper circuits to 3 independent plugs that the RV's could plug into.
If you want to run all 3 rigs at max output, you need a giant generator.
Assuming you are willing to be more modest, you can cut that back quite a bit.
An aircon unit will typically pull around 1500w continuous, so 5 units would be about 7500w. You need some additional overhead for other misc. loads and to cover startup loads, so maybe call it 10-12kw...no where close to 30kw.
Of course, if this is northern Michigan, you can probably get away with the 50amp rigs using a single air/con unit (living area during the day/bedroom at night), this would cut your demand back to 4500w rounded up to maybe 6-7kw.
We know some folks who do 3 30amp rigs on a 7kw generator. Seems to work fine.
PS: I would check on pulling power from the grid if you can get it but even up north don't be surprised if they don't want to provide it without you pulling a residential or business permit to build something.