H2oSprt wrote:
So it's an Atwood heater model 1522. The heater will blow air, auto igniter will click, I can feel a burst of hot air and then it will go out. The code on the heater reads incomplete ignition. I took it apart today, it's not dirty everything looks fine. My buddy thinks it's a circuit board issue. Might try replacing that next.
You should hear the flame, it is quite noisy.
There is a delay that occurs from when the fan starts to blow and then ignition. Sounds like you got to that point....
Here is the sequence for your 1522:
3. As the valve opens, the board sends a high voltage
spark to the electrode at the burner. The board detects the presence of a flame. If the flame is not sensed after approximately six seconds, the board will lock out (three try for ignition, one hour lockout and then three retry), shutting off power to the valve.
4. If the system does not ignite and the thermostat remains closed, the blower will remain on until the thermostat is reset manually.
Here is a link to the PDF service document for the 1522, I do not know which options you have but the call for heat is the same..
A reminder to thank Bryant's RV for providing unselfishly the many helpful documents he provides...
http://bryantrv.com/docs2/docs/hflamefurn04.pdf
http://bryantrv.com/docs2/docs/hflamefurn04.pdfFor all of you reading this... Bryant's rv has an excellent website with lots of documents and parts....