My trailer is parked under a metal carport on a dirt pad covered with rock. It has been raining and the ground under the rock is damp or wet, depending on where you are under the carport. Last evening, I was laying on my back on the rock, poking around the trailer skirting and I felt an electrical tingle where my arm was touching the metal trailer skirting. I had never noticed any problem like this in the past, not to say it didn't exist, but I had never experienced it. Got out my circuit tester, the plug-in type with the lights, and start testing the receptacles in the trailer, the extension cord from the garage to the trailer, and the garage. Everything tests 'fine'. The trailer has a hard wired surge protector, Surge Guard brand, and the indicator that there might be a problem on the protector is not lit up. I also have an Electracheck monitor to alert me to problems, bot nothing detected there either. Immediately disconnected from shore power.

This morning, I plugged in the trailer to shore power after verifying that the male end of the shore power cord was wired correctly. I get out the multi-meter and test for AC voltage between the trailer skirting and placed the ground-side tester probe into ground (mud under the rock) and I get a reading of .245 volts. When the ground point is changed to the carport supports which have metal rebar driven into the ground about 3 ft, reading rises slightly to .260 volts AC. Checking with extension cord un-plugged, reading was .130V AC. (Definitely didn't expect to see that.) Did a recheck of all the receptacles with the light-type circuit tester and everything tests OK. Turned off battery switch - no change.

What is the problem here? I wouldn't think you would feel about 1/4 of a volt, but I did, at least when the ground is damp. How could there be AC Voltage (as small as it is) when the trailer is not plugged into shore power? Where to start? How does one figure this thing out?
25 REPLIES 25

Salvo
Explorer
Explorer
I can't believe I'm responding to this nonsense!

You're missing basic electricity theory! Let me school you. The 12V battery is isolated from earth ground. There will never, ever be a current between the isolated battery within a trailer and earth ground.

MEXICOWANDERER wrote:
Seรฑor I may be at a disadvantage because even a single flashlight battery will rudely tingle the skin on the inside of my forearm when the skin is damp. Not a slight tingle either. The human body is weird. Not all individuals are built the same.

MrWizard
Moderator
Moderator
you have a reading when unplugged
then it is some kind of induction, RF, underground utility etc..
the only way to eliminate this is grounding the RV to earth ground
and this is NOT a 3ft stake in dry ground, or posts set in concrete
this is an 8ft ground rod into earth where it stays damp

Ron Nielson wrote:
MrWizard wrote:
check the electric ground to earth potential at the outlet the 5vr is plugged into

you might find zero volts
if so your situation is as stated in a previous post
capacitance effect, long cord, wires in rv, rv isolated from earth ground


My electrical problem occurs whether the trailer is attached to shore power or not. Is it possible that the extension cord or the outlet is the problem? I would not think so, but then I'm an electrical novice so my vote doesn't count for much.

Just makes sense to me that if there is electricity on the trailer skin, and the trailer is NOT attached in any way to shore power, then there's nothing on the shore power side of the house causing the problem.
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

MEXICOWANDERER
Explorer
Explorer
Seรฑor I may be at a disadvantage because even a single flashlight battery will rudely tingle the skin on the inside of my forearm when the skin is damp. Not a slight tingle either. The human body is weird. Not all individuals are built the same.

But, I heartily agree with your source of origin diagnosis. Correctly earth grounding the RV will result on 0.00 volts when disconnected or connected.

Place a spiral of magnet wire beneath a high tension power line and two things will happen. The coil of wire will develop a surprising amount of electrical power and secondly if discovered, the utility will indeed criminally prosecute for theft of electricity.

Salvo
Explorer
Explorer
Again, if nothing is connected to trailer (with inverter off), and you are measuring a small ac voltage then it's coming from radio waves. The closer you're to a transmitter, the greater the voltage.

I measure about 0.1Vac from chassis to ground on my rv. This is normal!

You won't get any tingle from that though.

Ron Nielson wrote:


My electrical problem occurs whether the trailer is attached to shore power or not.

MEXICOWANDERER
Explorer
Explorer
Something is amiss with drinking water passing through a length of PPE hose carrying 2-volts. The ultimate potentials would have to be enormous or mississippi river mud would have to be involved. It is standard practice to water washdown 12.5 KV distribution insulators with a stream of high pressure water.

Moot points all of this if the RV chassis is actually earth grounded. Course not eveeyone got an A in Pound-A-Peg. Mt stake is U-shaped, fluorescent red and I carry a D handle puller for yanking the stake out in seconds. All re-bar.

Ron_Nielson
Explorer
Explorer
MrWizard wrote:
check the electric ground to earth potential at the outlet the 5vr is plugged into

you might find zero volts
if so your situation is as stated in a previous post
capacitance effect, long cord, wires in rv, rv isolated from earth ground


My electrical problem occurs whether the trailer is attached to shore power or not. Is it possible that the extension cord or the outlet is the problem? I would not think so, but then I'm an electrical novice so my vote doesn't count for much.

Just makes sense to me that if there is electricity on the trailer skin, and the trailer is NOT attached in any way to shore power, then there's nothing on the shore power side of the house causing the problem.

Ron_Nielson
Explorer
Explorer
rekoj71

Great information about the problem you had (I NEVER would have guessed what your problem was found to be) and many thanks for the link. I'm working my way thru the posts now.

You asked about water piping to the trailer; no water going to the trailer at all.

MrWizard
Moderator
Moderator
check the electric ground to earth potential at the outlet the 5vr is plugged into

you might find zero volts
if so your situation is as stated in a previous post
capacitance effect, long cord, wires in rv, rv isolated from earth ground
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

MrWizard
Moderator
Moderator
so the 5vr is isolated from physical ground and electrically touching the earth
so any voltage potential between the ground wire in the cord (which is supposed to be at earth ground potential) which connects to the skin via frame ground at the breaker panel
is available between skin and earth
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

Ron_Nielson
Explorer
Explorer
Harvard wrote:
Can we assume the voltage from the RV chassis to earth is the same as the RV chassis to the car port?

There is some difference in the readings between the earth/dirt/mud under the trailer on the one hand and the carport vertical structures (2 1/4" square tubing, mounted on concrete piers sunk 4' into the ground). The readings to the carport are higher.

Harvard wrote:

Also, is the RV tongue jack making a conductive path from the RV chassis to earth or is it sitting on a non conductor?

The 5th wheel landing legs and also the rear stabilizers rest on 13" tall wooden guard rail timbers, then on concrete block on top of the rock which covers the entire carport and approach area. So very little conductive capacity there.

rekoj71
Explorer
Explorer
I just had this problem, even with the electrical cord, unplugged and laying on the ground and with no generator running. You can read about it here, but it is pretty long.
http://www.rv.net/forum/index.cfm/fuseaction/thread/tid/28447947/srt/pa/pging/1/page/1

In a nut shell I found about 5VAC with the RV plugged in and the circuit breaker turned off, and about 2VAC with it unplugged and couldn't figure out why for the longest time. The 5VAC ended up being sent into the RV by the ground connector in the plug coming from the campground electrical panel (campground fixed), and the 2VAC that I had even when the RV was unplugged was coming from the water supply. Yep that's right, the spigot, which of course some people use underground water pipes for a ground, was putting off almost 2VAC and it was carrying through the water and making an electrical connection to the frame of my RV (probably in the grounded water pump) that I was able to see on a multi meter when connected to bare metal on my RV and the other end stuck in the mud. They haven't figured out where that's coming from yet but from some other things I've read 2V or less might be felt if touching bare metal with wet hands and standing in bare feet in a puddle, but shouldn't hurt you (I hope). I was able to feel the 5VAC but now that that is fixed I haven't felt the 2V lately, but I haven't really tried to test it after a rain.
Are you connected to water at your house? Might try there.

Harvard
Explorer
Explorer
Can we assume the voltage from the RV chassis to earth is the same as the RV chassis to the car port?

Also, is the RV tongue jack making a conductive path from the RV chassis to earth or is it sitting on a non conductor?

Ron_Nielson
Explorer
Explorer
westend wrote:
Could it be that the wet conditions offered a path to ground along with the typical RV grounding? You would also need the power to have some type of open so that the ground would be part of the current path.

With the trailer disconnected from shore connection and having no inverter, there is no way to have AC from the RV to earth. That is a false reading from your tester.


You know, that really makes sense, and it was just what I was thinking. Must be a bad meter.

Well, I decided to take a simple test light, one side to power (my trailer skirting) one side to ground (mud under the rocks under the trailer) and see what happens.

Here's what happens: a small, but definite, light shows up in the tester! There IS electricity there. Meter reading is looking better all the time. Meter says electricity; light confirms electricity.

If only I knew the source of the electricity. I'm going to work on it some more tomorrow.

MEXICOWANDERER
Explorer
Explorer
MrWizard wrote:
Mex
are saying, i said ground stakes are nuts
or
are you telling me somebody else said that

i have never said not to use ground stakes with UTILITY power

i am against bonding neutral and ground on portable generators
because that creates just this kind of problem the OP is having


Oh heck no. But I have enough culture not to sling names. "Someone Else" spent a paragraph ridiculing my practice "pounding ground stakes" to GUARANTEE a safety ground. And that person with his electronics background should have remained silent rather than ridicule. A person that ridicules someone else's idea should include WHY the idea is absurd enough to warrant ridicule. Simple statements of opinion should be stated as opinion. It takrles a lot of real world experience to gain the title EXPERT legitimately. And from the posts I read we have several on this site. Anyone who documents experiences with RV components is far more credible than someone who blurts out an extremely strong opinion based on zero facts. There are tens of dozens of lurkers reading this forum and when a poster starts in with fiction I address my responses to the lurkers as well as members. When I do not know something I make it clear then ask questions. Storage batteries alternators and large generators I am quite familiar with. Sorry for the confusion Mr Wizard. If it's any consolation I read and re-read your responses. One of the truly reliable sources of info.