sjturbo
Sep 26, 2014Explorer
The 30amp shore service would only be plugged in when charging the batteries during boondocking. The inverter would not be powered up at that time.
Sorry MW I must have a short between the headset but I don't understand how this would look in a diagram or how I would hook it up based on your explanation. I agree the Transfer switch is likely lower quality but much easier to understand.
SM, are you responding to MW or me?
MEXICOWANDERER wrote:
A pair of common DPDT 120vac relays rated at 30 amperes can safely pass sixty amps and be used as a transfer relay. Wire them individually, one relay, both poles for the hot, the other relay both poles carries only neutral.
On the Kelley, I used six relays so as to provide 60 amperes capacity 3 phase 240 power. Those relays had 240 volt coils. A GE transformer converted single phase down to 60 amperes of 120 volt AC. When they were connected to the dock, and needed refrigeration they cranked up the Allis Chalmers 60 KW gensets and paralleled them. Shore power switching was automatic. The shore power cord was 4/4 cable, a little bulky.
There is ZERO reason to be forced to settle for garbage transfer switch relays, IMHO. The integral relay in my Trace 4024 has been neutered because it is a joke compared to the 6" X 6" box sitting next to the inverter.
Sorry MW I must have a short between the headset but I don't understand how this would look in a diagram or how I would hook it up based on your explanation. I agree the Transfer switch is likely lower quality but much easier to understand.
SM, are you responding to MW or me?