DrewE wrote:
Edit: Just noticed the 20A outlet there. Is that on the same 30A circuit (without a 15 or 20A breaker protecting it)? If so, that's definitely not up to code and a bit of a concern; the receptacle is underrated for the circuit's ampacity.
My S&B house has a bunch of 15 amp outlets on a 20 amp breaker. The receptacles are undersized for the circuit's ampacity too. As long as the wires going to the 20 amp outlet are sized for 30 amps, I wouldn't loose sleep over it.