We have moved on from rewiring my friends solar system. He's somewhat disappointed in Blue Skys method of only letting you see ah used and battery state of charge AFTER the system is 100% charged. I told him they all do things differently.

So now we are moving on to his next problem. He has said for a while now that he keeps getting shocked. I questioned him more on it and started checking things and the frame is bonded or there is a short of some type. After cleaning up some of the wiring in the converter power center we moved on to the inverter and sub panel.

I read his manual and it appears that magnum uses a relay to make or break the bond depending on if a generator or shore power are used. In the case of shore power the bond is at the pedestal. So on one page they seem to say that a bond is always needed but also say that under certain jurisdictions or situations it's not used.
I would take that to mean in RV's.

When not using the bond/relay system they say to unplug the green connector in the terminal strip area to disable it. I did that and the hot to frame dropped from 117 to 47 volts. The neutral bar to frame now reads 70 volts. Next step is remove the house panel feed wires to the inverter and try to isolate further.

I also want to see if 2 of the ground/bare wires in the magnum terminal strip are actually bonded???