dougrainer wrote:3 tons wrote:dougrainer wrote:pianotuna wrote:
I'd go for 13500 as they can be run on a 15 amp circuit.
A 13.5 Brisk air pulls 13.1 amps at 95 degrees.
A 15k Brisk air pulls 14.2 amps at 95 degrees
So, why can't you run either on a 15 amp circuit????????????? Doug
Doug, my Coleman 11k Mach 1 P.S. is rated at 9.0 running amps with Lo-fan, but using a clamp-on meter (on source hot wire), I consistantly measure about 11.6a...Can you suggest a way to measure for winding leakage?
Thanks
No, I have no way to determine leakage Never heard that term or problem. YOUR RVP is a specific LOW amp RVP designed for 30 amp dual AC systems. The OP was asking about Dometic systems. Doug
Got it, Thanks.