Thanks folks. As usual the forum has been a big help.
In summary, to replace my 50% depleted 210Ah battery bank back up to 90% with the PD9260:
1) using the graph, go for 2' 20" at 14.4V
2) using the approx. 105/50 = ~2 hrs at 14.4V
3) Another recommendation: 2hrs at 14.4V then 1 hr at 13.6V
4) Monitor voltage. When 14.4V is reached, continue charging at 14.4V for one more hour.
I'll give it a go, monitoring V and Time and see what happens.
There does seem to be a difference of opinion as to what/when the PD9260 will do after being forced into bulk mode. Will it eventually detect that the batteries are close to 90% full and switch out of bulk earlier than I want or just keep on going at 14.4V? I'll keep an eye on that too.
Cheers!