theoldwizard1 wrote:
ScottG wrote:
I know of nothing in the NEC that says you cannot have two 50A receptacles on one 50A circuit ...
What I was trying to suggest is replacing the first (existing) pedestal with a sub panel. Then you can run multiple 240V circuits off of that, as long as they each have their own pair of breakers.
As other alluded to, modern campground pedestals are typically "looped" which means that large branch circuit wires leave a distribution panel, then travel from one pedestal to the next. Meaning that there are multiple pedestals on the same breaker. There are lugs inside that allow large conductors to be attached to the pedestal bus bars. Using this system, one breaker, feeding one set of conductors, feeds multiple pedestals. So, to answer the OP's question, it's definite maybe. It would depend on the results of having a qualified person review the existing installation, and determining IF that loop has suitable capacity for another pedestal. Depending on the number of pedestals on the loop, the conductor and breaker size, and the total wire length. All critical info. in determining the answer.
OTOH, older facilities, (and even a few modern ones) can also have dedicated branch circuit breakers and wiring run to each site. This can be a result of a local backwoods electrician, who didn't have a clue as to how to design an NEC approved RV park system, or somebody who really overdid the job, and didn't want the remote possibility of overloaded loops.
Whatever the answer to the OPs question, it's not going to be found here. It takes a qualified person, on site, who can open things up, and determine exactly HOW this specific facility was wired, and has the knowledge regarding what can, and can't be done, with that info. At that point the answer rests on things like conductor sizing, total voltage loss, and load calculations.