red31 wrote:
is that @ 14.0v or 14.7v? , '14.7'
I'd rather dance on the side of slight overcharge than constant undercharge.
โSep-05-2017 10:50 PM
outwestbound wrote:
I have no knowledge in this particular area, but why would the sealed battery profile have no equalization? This poses no risk if they get equalized every 29 days in the flooded profile?
I decided to stay 12Vdc on the bank. Too much brain damage to change!
โSep-05-2017 08:04 PM
โSep-05-2017 07:57 PM
โSep-05-2017 07:00 PM
pianotuna wrote:
Hi BFL13,
Equalization should only be done on AGM jars when loss of capacity is noticed. It needs to be done gingerly while monitoring temperatures and amperage draw. Charge voltage must be close to the gassing voltage (which is temperature dependent) but should NEVER exceed the gassing voltage. This has the quaint name of "dancing on the needles".
this equalization process is what concerns me about setting the BZ controllers to flooded, cuz it seems to say that it will equalize every 29 days @ 14.9Vdc. I'll call BZ and see if I can set equalization on manual for the flooded profile, if this makes sense.
โSep-05-2017 06:48 PM
BFL13 wrote:
Don't forget you have to add more AH in than went out just to stay even. Charging efficiency. That varies over the SOC range. On my Trimetric monitor I find I need to go to about 15AH "over" to get to the point where the batts (about 430AH worth of open flooded) are full by hydrometer count.
The Tri has an adjustment for that if you fiddle with it and every day were the same. (they aren't of course) I don't bother. If it gets to about + 15AH and solar is done for the day, I reset the Tri AH to zero. (on solar don't leave the Tri in auto-reset!) If it doesn't get that high, as is often the case on partly cloudy days, I don't reset the Tri. Only reset when you know your batts are full---not when the bogus Tri instructions say "full" is.
โSep-05-2017 06:41 PM
pianotuna wrote:
outboundwest,
The Magnum running flat out at 125 amps of charging only draws 15 amps. I think that was pretty clever of them--because it means you can charge at full bore on a 15 amp shore power supply.
In real life, I limit mine to 12 amps, because I don't believe in drawing more than 80% for long periods of time. This also limits my charging amps to the maximum my bank can safely accept.
On your bank, fully charged would be when the rate reaches between 8 and 9 amps.
โSep-05-2017 06:41 PM
โSep-05-2017 06:41 PM
pianotuna wrote:
The bank is AGM and they start to taper at about 95% state of charge. The bank is 830 amps so the last 5% is about 41.5 amps. He gets 55 less the 7.3.
โSep-05-2017 06:25 PM
pianotuna wrote:
outboundwest,
The Magnum running flat out at 125 amps of charging only draws 15 amps. I think that was pretty clever of them--because it means you can charge at full bore on a 15 amp shore power supply.
In real life, I limit mine to 12 amps, because I don't believe in drawing more than 80% for long periods of time. This also limits my charging amps to the maximum my bank can safely accept.
On your bank, fully charged would be when the rate reaches between 8 and 9 amps.
โSep-05-2017 06:20 PM
BFL13 wrote:
Slow death by gradual sulfation is the fate of every battery, but you can speed that up by leaving them less than fully charged. It is only "damage" if it happens too soon for your battery budget. How much effort you put into caring for the batts is situational to your circumstances and the scenario.
The ONLY way to know if an AGM is truly full on a recharge is to observe the amps it accepts at the end of the recharge while the battery has no load on it.
You must have an ammeter and a voltmeter.
The regularly scheduled "equalization" on some chargers' profiles like once a week or once a month is not really a desulfation level equalization at all. It is just a dose of the regular "bulk" voltage of 14.x to prevent stratification of a flooded battery. N/A to AGMs AFAIK.
You have serious long drawn out tapering of the amps between 95-100% recharge so getting to proper full is not easy. Especially when the usual blurbs say "full" is when amps get down to about 2% of bank capacity in AH. That is maybe 98% SOC depending. So they are inviting you to be sulfated sooner than you might like.