Dave in Central NC wrote:I think you have a real safety hazard here. I don't know all the details and it's slightly complicated, so I could be making some wrong assumptions, one of which is that the inverter is in the truck. The result of the cheater plug working says that something goes wrong when the inverter's case is connected to the RV's grounding system.
The cheater plug gets the 2,000w inverter working.
โJun-30-2020 10:04 AM
Tom_M wrote:
From the Samlex website FAQ page:
"In some inverters designed for portable use, the two current carrying conductors connected to the "Line/Live/Hot" slot and the "Neutral / Return / Cold" slot of the receptacle ( for example, 15 A NEMA5-15R) are isolated from the metal chassis of the inverter. In these inverters, none of the two poles can be called Neutral as both these poles are isolated from the chassis of the inverter. Both the Line and Neutral slots of the receptacle will be at an elevated voltage with respect to the chassis - normally around 60 VAC (Half of the voltage between the two current carrying conductors). Hence, do not touch the neutral slot of the receptacle!
These types of inverters are designed to be connected directly to the AC loads. These are not designed to be permanently installed into household or recreational vehicle AC distribution wiring. As this type of connection / installation can not be classified as a permanent installation, the NEC requirement of grounded distribution system doesn't strictly apply."
https://www.samlexamerica.com/support/faqs/faq16.aspx
Try the cheater plug just to check if you have a neutral/ground bonding issue.
โJun-30-2020 09:47 AM
road-runner wrote:
Does the inverter shut down if you plug the 4.5 watt bulb directly into it, instead of through the shore power cord? You might have a load in the RV you don't realize. Water heater was mentioned. Other easily overlooked loads are the fridge and power converter. A basic and necessary troubleshooting step is to measure the DC voltage at the inverter input connections.
โJun-30-2020 09:46 AM
โJun-30-2020 09:17 AM
โJun-30-2020 08:49 AM
โJun-30-2020 08:40 AM
BFL13 wrote:
Want does "works" mean? You are getting low voltage alarm and shut down with the 2000w but not with the 800w.
Are you trying the 2000w with a big load like the water heater on electric, but not when using the 800w? Does the 2000w "work" with the same load as the 800w?
If all it is that makes the 2000w not "work" is a big load, you can reduce the voltage drop so it stays above 11v under load, by using fatter wire between inverter and battery bank, balancing the bank better with no "downstream batteries", and making sure the batteries are well charged up (needs an hydrometer for that to be sure)
BTW that red plug above is not supposed to be used in the Code ISTR.