time2roll
Mar 08, 2016Nomad
Deleted
I misread the high voltage protection :(
Actually the controller starts to derate long before even 145 volts. See graph in the operators manual.
Best to follow the original plan and string calculation with the 72 cell panels and keep the panels in parallel.
For 3 in series it is best to stick with 60 cell panels.
I misread the high voltage protection :(
Actually the controller starts to derate long before even 145 volts. See graph in the operators manual.
Best to follow the original plan and string calculation with the 72 cell panels and keep the panels in parallel.
For 3 in series it is best to stick with 60 cell panels.