DancinCampers wrote:
If leaving the cord plugged in to generator, just turn main breaker off before starting gen, then after gen comes up to speed turn main breaker on.
โFeb-24-2018 08:20 AM
โJan-30-2018 04:04 AM
j-d wrote:
I'd be afraid to use a pair of SPDT relays in place of a single DPDT. I can't draw a diagram to back the thought up, but it seems that if one relay "picked" and the other did not (say a coil failure), we could end up with problems.
As you deliberate this project, bear in mind there are entry level 30-Amp ATS units starting around $50.
If the genset is a recent model like ONAN 4KY, it won't supply AC to the ATS (or the coil in a home made one) until its logic board verifies it's good to go. So an ATS with its own power evaluation would be redundant.
โJan-09-2018 10:05 AM
โJan-09-2018 05:42 AM
โJan-05-2018 12:55 PM
โJan-05-2018 09:22 AM
โJan-05-2018 09:16 AM
โJan-05-2018 08:38 AM
Tom_M wrote:Jim@HiTek wrote:It appears that this contactor is a single through. A double throw (DPDT) would be needed for a transfer switch.
And here's one relay that Amazon carries that would work:
30 Amp contactor
Make sure that the NC and NO contacts are the same current rating.
โJan-05-2018 07:48 AM
Jim@HiTek wrote:It appears that this contactor is a single through. A double throw (DPDT) would be needed for a transfer switch.
And here's one relay that Amazon carries that would work:
30 Amp contactor
โJan-05-2018 06:35 AM
โJan-05-2018 06:06 AM
โJan-05-2018 05:46 AM
Jim@HiTek wrote:
Here's that schematic of a home built ATS (Automatic Transfer Switch). It can be either a single DPDT, or two SPDT relays with the coils (and only the coils) wired in parallel. They can be 30 amp too if you tend to be frugal with electrical usage. The grounds are just all connected together. I'd recommend using the best high quality parts when connecting things together. As it's wired, the genset has to come up to speed and properly present it's voltage to the relay before it operates. So no delay needed for most applications.
When operating, it's important to note that this is a 'dumb' ATS, not like today's smart devices that sense when the AC voltage passes through ground before it switches so there's never a spark or problems downstream with any live electronic devices like TVs or computers. Just like the old days where you had to shut most stuff down before starting the genset.
And finally, I'm aware the word 'continuous' is spelled wrong on the drawing.