Outside of specification volts per hertz is DEATH to an AC generator voltage regulator. So today's voltage regulators established 55 Hz is a minimum generator speed at which the regulator will force field a generator to maintain voltage.
The problem with timer based protection is that it does nothing to protect against underspeed. It is assumption based protection and assumption based protection is as hazardous as assumption based battery state of charge. Configuring a voltage regulator for a larger generator should include the Volts per Hz inherent protection of a voltage regulator design.
The problem with timer based protection is that it does nothing to protect against underspeed. It is assumption based protection and assumption based protection is as hazardous as assumption based battery state of charge. Configuring a voltage regulator for a larger generator should include the Volts per Hz inherent protection of a voltage regulator design.