time2roll wrote:
BFL13 wrote:
The no go with 55 and 75 is a puzzle. It pops the breaker(s) immediately.
is it a load issue or a GFCI issue?
Set the voltage same as the battery (26v?) and try again.
No, this is with the battery bank as 12v. The 55 and the 75 run perfectly from the Honda 3000 individually, but add one to the other and it pops the Honda's overload, but the engine keeps running. Then you have to shut down the generator's engine and start over as how to reset it.
Same thing with the 75 (non-PF) and the PFed 100.
When you add the non-PFed 55 to the running 100 it just revs up the gen a little more and you see 155 on the Trimetric, no sweat. Seems that is about max in VA for my Honda 3000 (14 years old at sea level)