โJun-15-2013 10:15 PM
โJun-25-2013 03:35 PM
Had the same issue a couple of years ago.....but the cause for me was the 120v heating unit on my water heater. Evidently, this causes this problem on a regular basis. If you have a gas/electric water heater, it's worth checking out ad easily fixed.A fault in the water heater cannot cause a non-hazardous tingle between an RV and earth ground. The only thing indicated by a non-hazardous tingle is an ungrounded RV chassis. A water heater fault combined with an ungrounded chassis creates a very hazardous situation, which is why a good ground connection is so important. The water heater fault will however cause a shore power GFCI to trip when the chassis is properly grounded.
โJun-25-2013 03:08 PM
That's true now, wasn't in the not-too-distant past for detached buildings. According to this forum thread 3-wire feeds to existing detached buildings the change occurred at the 2005 NEC to 2008 NEC transition. Haven't researched it myself.
My understanding of the NEC is that neutral and ground NEVER get bonded at subpanels, that's why you don't do it in an RV, it's basically a sub panel.
โJun-25-2013 03:02 PM
โJun-25-2013 02:23 PM
โJun-25-2013 01:27 PM
Wayne Dohnal wrote:
I have an outbuilding that's fed from the main panel in the house but has its own independent grounding electrode. There's a neutral-ground bond at the main service entrance, and another at the outbuilding.
โJun-25-2013 11:18 AM
โJun-25-2013 09:44 AM
โJun-25-2013 06:36 AM
MPD56 wrote:
Harvard: There are lots of what if here. The diagram in your last post although could work, it is probably not the way the Power Company has connected it physically. If you have a voltage drop that can be read with a meter, then you will get current flow through a resistive and/or impedance electrical path.
If an over head bare high voltage power line had broke and is lying on the ground, you canโt assume the earth is a pure conductor (0 resistances to current flow). This is the reason why grounding and bonding methods are so important. The powers that make the Electrical Codes canโt make it 100% safe.
The OP trailer could have a bonding or grounding problem that is causing him to feel a shock. I say โcouldโ because what if the wet ground was providing the 18 volts from the power cord sitting in the water and the chassis of his trailer is a less resistance path to the sourceโs safety ground, meaning his trailer chassis is wired properly? At some time or another youโre going to read a voltage from chassis to earth ground, the codeโs wiring methods are there to hopefully reduce that voltage so the no harm comes to us. From a keyboard, I canโt assume were the OPโs problem is, but he knows he had a problem and is taking steps to correct it.
FYI:
The power company use meters to detect ground fault currents and they are not volt meters from a hardware store. A GFI receptacle doesnโt monitor voltage to ground. 18 volts I wouldnโt think a human would feel a strong tingle, at least I donโt? There is a good reason why the powerโs to be picked no more then 120 volts to ground and not a subject that can be taught on a RV Forum.
โJun-25-2013 06:26 AM
MEXICOWANDERER wrote:
Eddy currents.
What is your objective?
โJun-25-2013 05:31 AM
Harvard wrote:
For sure you have an open ground conductor. In other words, there is no continuity in the ground wire from the RV chassis to the power distribution Earth Grounding Rod. Be very suspicious of the "adaptors".
โJun-24-2013 01:50 PM
โJun-24-2013 11:08 AM
โJun-24-2013 08:17 AM
โJun-23-2013 08:42 AM