Forum Discussion
dougrainer
May 17, 2020Nomad
1. You have NOT removed all the wires from the hole for the Tstat.
2. You will NOT have "blue" wires at the tstat. The Blue wires are the 2 just for the furnace AT the furnace that go to the wall tstat and return
3. Most OEM's use standard home type Tstat multistrand wire to connect the Roof AC and to the furnace.
4. Usually they use the small 20 gauge wires---red and white to go from the furnace to the wall tstat.
5. When you have your type tstat, the one blue wire at the furnace that is 12 volt, it goes to the Roof AC control board in the AC. THAT wire is what supplies 12 volt power to the Roof AC control board and then DOWN to the wall tstsat. On other models, the blue 12 v wire goes to the wall tstat and then another wire then feeds the Roof AC for 12 volt power to the Roof AC. You need to get all the wires out of that small hole in the wall and odds are you will see a wire not connected. Doug
2. You will NOT have "blue" wires at the tstat. The Blue wires are the 2 just for the furnace AT the furnace that go to the wall tstat and return
3. Most OEM's use standard home type Tstat multistrand wire to connect the Roof AC and to the furnace.
4. Usually they use the small 20 gauge wires---red and white to go from the furnace to the wall tstat.
5. When you have your type tstat, the one blue wire at the furnace that is 12 volt, it goes to the Roof AC control board in the AC. THAT wire is what supplies 12 volt power to the Roof AC control board and then DOWN to the wall tstsat. On other models, the blue 12 v wire goes to the wall tstat and then another wire then feeds the Roof AC for 12 volt power to the Roof AC. You need to get all the wires out of that small hole in the wall and odds are you will see a wire not connected. Doug