mbrower wrote:
I finally got around to installing an inverter and have question concerning transfer switch. A little information on what I have. I bought a 50A progressive dynamics xfer switch that I wired with priority to shore power instead of inverter/generator. I took the time delay out so the switch will transfer power instantly with no loads dropping out. I ran the power for the AC's and hot water heater through a contactor that is actuated by shore power so when power is switched to inverter, both ACs and water heater are open circuits. I also ran a separate 30A marine plug to the front of the camper to power camper from portable generator and tied it into the inverter circuit via a 30A transfer switch with priority to inverter and a time delay switch to generator.
Everything works well configured this way but I do have concerns with the 50A relay switching loads backwards. Progressive dynamics have been little help as to drawbacks if any and I was seeking wisdom from fellow campers. Any information would be appreciated.
You are defeating the purpose of the transfer switch.
You said that you wired with "priority to shore power" which makes me think that you wired it differently from Progressive Dynamics design criteria. Your configuration will work by having the option of whether you want the power priority to be applied as in inverter/generator over shore power. By having a NO/NC contactor, you can only have one or other--not both at any given time . . .which is fine.
However, I'm concerned when you added a separate power input from a portable generator with a 30A plug. Power distribution systems designers take the time to figure out every scenario that can happen when their product hit the consumer. It would be a big mistake to oversimplify something that took considerable time for experts to examine every angle that might happen should their product are subjected to abuse. Unauthorized modification is one of them.
This is one reason engineers at Progressive Dynamics are not willing to commit. Say what you may but these are professionals who could be held accountable should their product cause harm or worse.
One scenario that could be catastrophic is: although you can be sure (after a good night's sleep and you haven't had one drink too many) that shore power is not applied when using the separate 30A marine plug.
What will happen if you forgot by having both sources applied to the rig?
The above could happen because you are using one NC contactor and a separate NO contactor feeding one common input.
If you have the marine 30A plug energized (along with the shore power plug) you will end up energizing the shore power distribution lines which could be deadly to utility workers.
This is where transfer switch becomes mandatory.
The above is just one scenario, but there could be more... cross feeding could also be a possibility.