Water Heater Gas Valve Stuck Open UPDATE-Bench Test

BFL13
Explorer II
Explorer II
Updated 25 May
--------

Was having trouble getting my 1991 OEM Atwood WH to light for months, worked sometimes, very frustrating. Got some parts off a newer WH including the gas valve and swapped things around and thought it was a success.

However, since then could smell propane a little, including inside the rig. No LP alarm, not that bad of a leak I guess. After much trouble shooting, I narrowed it down to be a gas smell at the burner end even though the WH was turned off. (For a while I was convinced it was at the gas inlet end and tried to fix that--more yellow tape, tighten--not it)

Had to be the outlet end. I tried to light it with a BBQ lighter, and it lit with a small blue flame that stayed on! I also found the seal where the gas line comes out front was not sealed properly, so that must have been how the smell got inside the rig. Fixed that.

Another clue was that when first lit, it made a bang so I suspected a "delayed ignition" type event where fuel accumulates before the spark. That can be very bad!

Swapped the old gas valve back in, and discovered its ground wire was loose so that was why it was not working right all that time before. All good now.

Sooo--the question is, with the newer gas valve (photo) how can it be stuck open? Can it be fixed so it can be kept as a spare, or is it toast?

Thanks.

Photo of newer valve that is stuck open



Photo of the OEM valve, now back in and working

1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.
12 REPLIES 12

CaptainLarry
Explorer
Explorer
Covered this ground once. There is a thread here that I started in 2014. Started a real fire storm of feedback. Ha! Valve still works 6 years later.

Search "Repair leaky White Rodgers gas valve in Attwood water heater" Maybe its blocked since it was so dangerous.

Sorry to be so cynical.

Stay Free Everyone!

BFL13
Explorer II
Explorer II
For those keeping score--- I wondered if maybe the valve was not in fact stuck open, but that there was 12v to it even when WH turned off.
If so, the same thing would be happening with the one in there now.

Removed valve pos wires from ECO terminal--no voltage at terminal (just a tiny bit), turned on WH, got the sparking clicks and voltage jumped to 13.x. Sparking ended, voltage back to a tiny bit.

So, OK there. No smell either! I am declaring victory on this one. All set for the next thing that happens. ๐Ÿ™‚
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

BFL13
Explorer II
Explorer II
Bench tested the stuck valve (just to see what happens)

Assumed it was still stuck open, removed the orifice--you can see the valve mechanisms inside--seem nice and shiny, clean.

Poured some mineral spirits down the inlet, nothing came out.

Put 12v to both pos wires at once and to the two green wires bolted together to the valve body. Loud click, remove 12v click, lots of clicking. You can see things moving in there.

Tried to pour some spirits in with the 12v power on---it came out the orifice end so it is open with 12v power on, as it should be.

Took both green wires off and put power to each one at a time--clicking with either one.

CONCLUSIONS
1. It was stuck open, so I must have banged it or whatever removing it and after that.
2. It works now and both solenoids are working.
3. Yes you can bench test a gas valve
4. I would not trust this one, but could use it as a temporary field repair spare, doing a smell test each time before lighting the WH so not to have a surprise delayed ignition event (explosion)
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Gdetrailer
Explorer III
Explorer III
Generally anything with propane connections/combustion chamber that is exposed to the outside air and sealed off from the inside, that propane will drop and hug the ground level and be dissipated by the wind or or if no wind will pool around the lowest level of the ground..

In other words most likely will not enter the inside of your RV to levels high enough to trigger a propane alarm unless you had a cylinder/regulator malfunction large enough to create a big heavy cloud of propane fast enough to engulf and surround your RV..

Propane alarm would be more like monitoring for propane pooling from INSIDE propane connections and in most cases your stove/oven connection and or valves.

BFL13
Explorer II
Explorer II
The floor level LP alarm didn't do any good at all. I tested it with real propane from a BBQ bottle and it worked, so that's fine, but it is nowhere near any of the three actual propane burners reached from outside access doors. The stovetop and oven is all that is inside.

Not sure what would have to happen to create a cloud of propane by the LP alarm inside in the middle of the RV at floor level. Have to be the stove I guess.

I have a fire alarm and a CO alarm up higher which also work when tested (no actual CO test done, but fire alarm goes off if smoke comes in the door when BBQing)
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Gdetrailer
Explorer III
Explorer III
BFL13 wrote:
If the fault is the valve won't open, you know something is wrong and will eventually find it . In this case with it stuck open, the WH worked ok and it was some time before I noticed anything was wrong-- can be dangerous.

So I need a routine check of the WH, fridge, and furnace to catch this a lot sooner after it happens if it happens again. Sniff test at least.


You have a 1991 appliance, a 29 yr old device which is exposed to the great outdoors.. From your pictures it has considerable rust on the DSI ignitor/flame detection parts. The valves you show have considerable amount of weathering, consistent with winter salted roads..

You HAVE gotten your money's worth out of it for sure.

I suspect any valve has the potential to fail in open or closed position, generally though electrical gas valves are supposed to fail in the closed position but hey, anything can happen. Things like moisture content in the propane supply can corrode the internal parts and the oils in the propane supply can gum up internal moving parts.

I would have to say, that given the age of your rig, just a periodic sniff test should still suffice, I wouldn't think you would have to check every day for the most part.

BFL13
Explorer II
Explorer II
If the fault is the valve won't open, you know something is wrong and will eventually find it . In this case with it stuck open, the WH worked ok and it was some time before I noticed anything was wrong-- can be dangerous.

So I need a routine check of the WH, fridge, and furnace to catch this a lot sooner after it happens if it happens again. Sniff test at least.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

dougrainer
Nomad
Nomad
1. Atwood Gas Valves(older) have a common problem with small leaks. Even with a dual solenoid. This is after years of operation. I always do a liquid bubble leak test FIRST on an Atwood Gas valve orifice when my manometer test shows a small leak on an older RV. I am right about 50% of the time.
2. There is no REAL law or regulation that states a Consumer CANNOT work on his Gas appliance or system. It is just NOT a safe practice to do. But, there are rules and regulations in a lot of States, that dictate you must be licensed to install/repair, gas appliances and systems/piping in a commercial activity. Failure to be licensed and something happens you can be sued. Also the Licensing Agency can fine you if you work on gas systems if the law requires you to be licensed.
3. Gas parts are not serviceable. You cannot even buy replacement individual valve parts. I WOULD NEVER ATTEMPT TO REPAIR ANY GAS VALVE, EVEN THO I KNOW WHAT I AM DOING AND I AM LICENSED. JUST NOT A SAFE PRACTICE. AND AGAINST TEXAS STATE LAW AND REGULATIONS. Doug

BFL13
Explorer II
Explorer II
Concur that I would not trust it if I got it working again.

How common is it for these valves to be stuck open? Should I worry about the older one back in there now? What about the valves for the fridge and furnace? Can they get stuck open?
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Gdetrailer
Explorer III
Explorer III
Hmm.. I wonder what happened to the poster from CA that always spouted off about the CA requirements for a "certified" propane technician to repair propane systems? Looks like you have voided CA "laws".. :E :B

I am with Old Biscuit, while there have been a couple of folks who have torn down and repaired those valves and gotten them to work. Unlike those folks I really do not feel they are worth gambling my life on.

I suspect however that valve may not be as reliable as it should be even if you do manage to repair it.. How comfortable are you with it once and a while leaking again down the road? Explosions can be sometimes fun, but not so much when it is something you are living in..

Sometimes it is money, time, safety ahead to replace with new rather than MacGyvering a mission critical part into working.

Chuck the leaky valve in the garbage and don't look back.

BFL13
Explorer II
Explorer II
Thanks. To bench test it, if I can get it unstuck with spray and banging on it, will it operate by putting 12v to the positive wires that go to the ECO and the "chassis" of the valve where the neg wires are connected?
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Old-Biscuit
Explorer II
Explorer II
LP System only has 0.4 psi so iof gas is leaking thru gas valve then it is NOT salvageable.

Takes BOTH solenoids to be energized to OPEN the gas valve
When DC is removed springs close the gas valve
Able to light and have small flame at gas valve means it is leaking thru with ONLY 0.4psi