โJul-16-2017 05:16 PM
โJul-19-2017 07:31 PM
MrWizard wrote:
power from a utility source, coming into a breaker
is NOT a back feed, you re mis-construing term, just because of the location of the breaker
anyway it does not apply to what you want to do
โJul-19-2017 07:28 PM
โJul-19-2017 07:13 PM
MrWizard wrote:
there is confusion
you mentioned 50amp. i thought you had a 50amprv
you mentioned (2) a/C
are you rewiring a 30 amp rv for 50amp
and yes. no generator, no TS
the input lugs, would be for input IF there was a meter and main before the panel
all RV's have a main breaker, "that is not a back feed"
I gave you the definition of back feed
feeding from someplace that is illegal
example : if you removed the current main breaker and installed another breaker box with the shore feed and the inverter feed and (2) breakers with a manual lockout selector so only one could be used
you could connect that to those input lugs at the bottom of the panel are currently 'unused' that would be safe and legal
your current use of the term 'back feed' can cause confusion, and mis-direction
code says there has to be an input breaker
that breaker can be in the panel (the one you have now) or outside the panel in another box (often done in commercial wiring, not done in RV's)
a main breaker in the panel like you have it is LEGAL CODE, not back feeding
but that is beside point (just clarification)
โJul-19-2017 06:55 PM
โJul-19-2017 06:35 PM
MrWizard wrote:
this keeps the neutral leg from being overloaded by an imbalance
โJul-19-2017 06:24 PM
Mr wizard wrote:
NO thats not back feeding
those are out put breakers going to the sub panel
Mr wizard wrote:
back feeding is when you bring hot "power in" from what is leagally and output circuit
Mr wizard wrote:
take a double ended suicide cord
plug end 'B' into an outlet in the RV
plug end 'A' into a shore outlet
THAT IS BACK FEEDING
Mr wizard wrote:
so the guy at fleetwood, messed up
and you re-balanced it..good
i never said not to re-balance
i said don't put all the heavy items on one leg
i would separate the (2) A/C they are the two big items most likely to be on for hours at a time thw other loads are more intermittent, this keeps the neutral leg from being overloaded by an imbalance
rearrange the other loads
having an a/c on the inverter leg won't hurt
you won't be running the a/c with out the genny or shore, not near as likely to forget as say the WH or fridge
tv, outlets, ceiling fan, MW, IMO must have for inverter
A/C can be on that circuit and the washer/fireplace IF you want, the victron pass thru will handle it when using genny or shore power and those are items not likely to be accidentally left on, or come on automatically (victron is an excellent choice)
and unless you have a Manual lock out breaker switch arrangement for generator and shore choice, there is a 50 amp 3pole TS someplace, mine is a big silver box in the electric bay, because my breakers are in the cabinet over the BED
Mr wizard wrote:
yes in some respect
but 30amp RV don't come with electric heat fireplace and washer dryers
and the (2) a/c only run on generator, RV is usually setup that only (1) a/c can be run on shore power, then its power management time for MW etc..
its not all run at the same time when the RV has 30amp main
โJul-19-2017 06:05 PM
Yes, I know houses have main breakers - except that they're not usually down in the the same breakers as all the branch circuits. They're usually up above the branch breakers and separated. However, if you feed a small subpanel in a garage that doesn't have main breakers and you use 2 breaker slots where branch circuits would go to feed the panel, that's backfeeding. I can tell you which one mine looks like
I hear what you are saying, and I don't disagree. However, it would seem your advice would be better vetted with Fleetwood, as they certainly didn't follow your advice. This is how my panel came wired from the factory (refer to photo above if you doubt it).
L1: GFI (15A) [most outlets in camper], A/C 1 (20A), A/C 2 (20A), Microwave (20A), Water heater (15A) ----- TOTAL: 90A
L2: Fireplace / Washer-Dryer (15A), Refrigerator (20A), Ceiling Fan (15A) [other outlets, TV, stereo], Converter (15A) ----- TOTAL: 65A
Would you call that balanced? Cuz I wouldn't. Moving AC1 and AC2 onto L2 and bringing the ceiling fan circuit over to L2 doesn't look like that big of a change to me. It looks better, in fact. The converter circuit would become a spare as the inverter would take over those duties. New "total" amperages would be:
Better than it was before. Besides, you guys running 120V only feed all the same stuff I have on both legs from 1 leg, and are limited to less current (usually 30 amps). I have two legs and each one can carry 66% more current than that. I understand what you are saying from a theoretical standpoint, but it isn't relevant in practice.
โJul-19-2017 05:31 PM
MrWizard wrote:
thinking 'not correct'
its normal to have a main breaker in a house.
this is 'not backfeeding'
MrWizard wrote:
moving loads around for 'balance is good'
moving loads so all high draw items are on ONE LEG is 'BAD'
especially since you want the (2) a/c on separate legs
wh on one leg, MW on the other leg
MrWizard wrote:
NO NO do not feed the bottom panel lugs from the inverter
there is way too much chance of blowing up the inverter from shore power or generator
MrWizard wrote:
get a 50 amp rv transfer switch
install it after the existing TS, us it to choose between (existing) or inverter
if you want to isolate circuits automatically, instead of remembering that certain things need LP only
then install a sub panel for the inverter circuits and move them there
โJul-19-2017 04:50 PM
โJul-19-2017 02:08 PM
โJul-19-2017 01:37 PM
โJul-18-2017 02:39 PM
โJul-18-2017 02:16 PM
LipschitzWrath wrote:
Not a lot of information out there so I figured I'd post here.
If like to add an inverter for my 5er, mainly to limit inconvenient trips out to get the generators running for small things. One of the first things that comes to mind is the coffee pot. That's about the only AC power we use in the morning.
โJul-18-2017 02:09 PM
CA Traveler wrote:
Power off, remove the CB panel and find out what circuits are on L1 and L2. Remove lights, speakers, etc and look for access. My cabinets have decorative inside panels that are held with wire brads and glue, easy to remove. You may need to remove under rig paneling for access. Interior walls are likely hollow. Iโve run wiring in exterior walls that have insulation. Check, be creative, etc.
Yes ATS = Automatic Transfer Switch, Victron let alone 2 is high dollar. How would you use one inverter for a whole house? Youโll need to switch those wires somehow.
Some charger/inverters have a built in ATS and CB protected outputs. No sub panel needed.
Many rigs have a built in gen and an ATS is used to automatically switch between shore power or gen power. So when you read about an ATS be clear about the application.
An charger/inverter can either charge the batteries from the charger or supply 120V from the inverter. It will automatically switch when it senses AC input but it does not do both at the same time. Some like separate units for various reasons but you have to manually select one or the other. Using the inverter output running from batteries to run the charger is a sure way to run down the batteries. No free energy.