The 30 amp controller can handle 30 amps. You need that ability when your panel can do 24 amps at STC so you can have the margin for when the panel does more than its ratings.
24 x 1.25 = 30 The panel and the controller are a "system" If you had enough panel to do 30 amps you would need a 30 x 1.25 = 37.5 so a 40 amp controller.
With PWM, you get panel Isc not Imp which has no meaning with PWM.
A 130w panel could have an Isc of 8.2 like my Sharp but some have more and some less Isc per watt at STC.
24 x 1.25 = 30 The panel and the controller are a "system" If you had enough panel to do 30 amps you would need a 30 x 1.25 = 37.5 so a 40 amp controller.
With PWM, you get panel Isc not Imp which has no meaning with PWM.
A 130w panel could have an Isc of 8.2 like my Sharp but some have more and some less Isc per watt at STC.