why don't Solar controller mfg/sellers use honest ratings

MrWizard
Moderator
Moderator
example most 30amp controllers are listed at 390w of panels

and 40amp controllers at 500w of panels

but we don't charge batteries at 12.0v we charge at 14v or higher

14v*30 amps 420w output, going to need more than that input

40a*14v 560w output to batteries, controller must handle at 600w input

500w with 17.5 actual output 12v nominal panels only equals 28.57 amps into and thru Controller NOT 40 amps

so will these controllers really handle the rated amps ? which means a much larger array than the stated max

or are they just blowing smoke..uykw

30 amp ? 390/17.5v = 22.28 amps max from the array
so what is it really a 25amp controller ?

30amps charge at 14v =420watts out , 17.5 * 30 = 525 input
you need 525w panels to get 30amps out at 14.0v

this of course does not included mpppt panels although the same mfg/sellers are doing the same thing playing loose with the words
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s
59 REPLIES 59

pianotuna
Nomad III
Nomad III
Hi Mr Wizard,

I prefer discreet devices, too, but 999 for a 3000 watt psw inverter is pretty good and having the ability to do 30 amps of solar is a definite bonus.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

Naio
Explorer II
Explorer II
pianotuna wrote:
This looks interesting--a combo inverter/charger/solar controller.

inverter charger and solar controller It can accept 30 amps on the solar side.


Cool find. Until I saw the $9oo price tag!

Edit: OIC, that is just what 3000 psw's cost.
3/4 timing in a DIY van conversion. Backroads, mountains, boondocking, sometimes big cities for a change of pace.

MrWizard
Moderator
Moderator
thats interesting, i don't think its practical for Rvs, at least not for me
AC charge is too low at 25amps,
i prefer discreet devices, easier to replace an item if some function fails
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

pianotuna
Nomad III
Nomad III
This looks interesting--a combo inverter/charger/solar controller.

inverter charger and solar controller It can accept 30 amps on the solar side.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

MrWizard
Moderator
Moderator
I don't think of voltage as being a problem with controllers
In most cases your panels in series is easily under the limit or you know it's over, especially with PWM where parallel is the norm, because you want amps not volts
With MPPT you do need to check that your series arrangement is under the controller limit
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

BFL13
Explorer II
Explorer II
It is not 1.25 for voltage as such, but you do have to leave margin in your controller's total Voc input limit for when Voc is higher than rated at STC.

You can calculate that from the coefficient in the panel spec for the coldest you expect to be using it.

Mr Wiz--"working amps" with PWM is Isc NOT the lower Imp figure you would use with MPPT. You would see this if you had tracking panels and checked panel Isc (disconnected) with amps to the battery (connected) --same amps amount.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

MrWizard
Moderator
Moderator
NEC says use a controller with a rating 25% more than your isc..not working amps which is less than Isc
I don't know how the output would ever reach that point
Unless maybe there was a dead short on the output at STC..?
And even then you could not exceed Isc

And morning star says the controller will handle 130% of the rated input and taper the amps
Which means NEC wants you to use 36amps Isc not the panel working amps for a 45amp controller that the MFG says will handle 58 amps input

Now I believe Morning star, I would have no qualms connecting 700w aka 41amps to that controller

But I would have second thoughts about some of these other controllers
The NEC and controller MFG are not using the same play book

There has got to be done middle ground for quality and price point
How long until the market sorts itself out
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

time2roll
Nomad
Nomad
With 41 amps Isc it would appear you need a PWM controller rated 51.25 amps minimum to meet NEC. That probably puts you at a 60 amp controller.

Those panels in series would need just 45 amp MPPT to meet NEC and not clip the amps. Actually if you rarely see 35 amps a 30 amp MPPT might be fine with minimal clipping. Still meets NEC.

There is no 125% applied to voltage that I am aware of.

MrWizard
Moderator
Moderator
what is the "Voltage" ?

again this is MPPT which will convert the volts to amps
for increased output
something that DOES NOT happen using PWM

all the cheap controllers are PWM, even the the 'fake' mppt are PWM
there is no 'overhead' conversion to more amps

smkettner wrote:
Yes this is on p8 of the TS MPPT manual:

To comply with the National Electric Code (NEC), the current rating of the controller must be
equal to or greater than 125% of the solar arrayโ€™s short circuit current output (Isc). Therefore, the
maximum allowable solar array input to the TriStar MPPT 150V controller for compliance with the
NEC is:
TS-MPPT-30: 24 amps Isc*
TS-MPPT-45: 36 amps Isc*
TS-MPPT-60: 48 amps Isc* *Solar array Isc @ STC


My array Isc is about 8 amps and 675 watts. Maybe another reason to go series.

TS MPPT manual
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

MEXICOWANDERER
Explorer
Explorer
Empty Nest, Soon wrote:
I have not looked that much at cheaper controllers, but the lack of a heat sink is one obvious difference. And yes, providing a heat sink at a reasonable cost should be easy. I canโ€™t explain why the market has not offered that.

But how about a Tri-star 45 for $161? http://www.ebay.com/itm/221681616399?_trksid=p2060353.m1438.l2649&ssPageName=STRK%3AMEBIDX%3AIT

Wayne


If you believe heat sinks are reasonable take a heat sink tour of eBay, electronics suppliers and manufacturers. The price them like they are manufactured from copper. And the cheap @#$/\&!, s don't even bother to black anodize them. A heatsink for a working MOSFET is not small. I am forced to use 7 fin 50X40 mm sinks for my LED buckers. Heat sinks are the bane of the LED industry. You hear screams THIRTY WATT LED LIGHT and find out it's driven at 20 watts with a hot as hell heat sink.

Working with newer electronics and their cost structure has really given me an education about heat sinks. Devices are taxed thermally to the bitter limit and of course the fluorescent tie & paisley shirt crowd lie like hell in order to sell merchandice. Welcome to the age of B.S. There's no one out there to trim their horns.

MrWizard
Moderator
Moderator
BTW,, for those interested
the Imp? Working amps,, for my current configuration is right at 41 amps

hoping to hit 35 amps at STC during testing this Sunday

i will have to put a load on the inverter to do so
maybe run the Vacuum cleaner
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

time2roll
Nomad
Nomad
Yes this is on p8 of the TS MPPT manual:

To comply with the National Electric Code (NEC), the current rating of the controller must be
equal to or greater than 125% of the solar arrayโ€™s short circuit current output (Isc). Therefore, the
maximum allowable solar array input to the TriStar MPPT 150V controller for compliance with the
NEC is:
TS-MPPT-30: 24 amps Isc*
TS-MPPT-45: 36 amps Isc*
TS-MPPT-60: 48 amps Isc* *Solar array Isc @ STC


My array Isc is about 8 amps and 675 watts. Maybe another reason to go series.

TS MPPT manual

MrWizard
Moderator
Moderator
That link is not working for me
But I did find this
To comply with the National Electric Code (NEC), the current rating of the controller for solar charging must be equal or greater than 125% of the solar arrayโ€™s short circuit current output (Isc). Therefore, the maximum allowable solar array input to the TriStar controller for compliance with the NEC is:
TS-45: 36 amps Isc
TS-60: 48 amps Isc


$142.25

http://www.ecodirect.com/mobile/product.aspx?ProductCode=Morningstar%2DTriStar%2DTS%2D45&gclid=CM7M...
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s