It is not 1.25 for voltage as such, but you do have to leave margin in your controller's total Voc input limit for when Voc is higher than rated at STC.
You can calculate that from the coefficient in the panel spec for the coldest you expect to be using it.
Mr Wiz--"working amps" with PWM is Isc NOT the lower Imp figure you would use with MPPT. You would see this if you had tracking panels and checked panel Isc (disconnected) with amps to the battery (connected) --same amps amount.
You can calculate that from the coefficient in the panel spec for the coldest you expect to be using it.
Mr Wiz--"working amps" with PWM is Isc NOT the lower Imp figure you would use with MPPT. You would see this if you had tracking panels and checked panel Isc (disconnected) with amps to the battery (connected) --same amps amount.