Anybody has a good calculator for wire gauge? I need to do a wire run of 200ft buried wire. I can do 50amps or 30amps. Any advise will be greatly appreciated!
Alfa SeeYa
Life rocks when your home rolls
25 REPLIES 25

time2roll
Nomad
Nomad
SAR Tracker wrote:
wire size calculator (dot) net


If you use 200', 240v, 35 amps, 3% in the calculator you only need #6 wire. This still allows two large draw items on each side of the panel and plenty of ampacity if you draw close to 50 amps for a few minutes.

Matt_Colie
Explorer II
Explorer II
Sorry guys,

I just read the whole thread and I can't sit back any longer.

First: If you don't buy enough copper to do the job right, you may save money now and you will probably pay for it forever......

Second: A 3% voltage drop is meaningless. Voltage drop is Volts Lost and irrespective of the starting terminal voltage. Most of these tables give you that 3% number and don't mention that this is only one way. There has to be a return.

Your current coach is 30A? It is a waste of time to set up for 30. Put in wire for 50. Use 3 conductors but you can save on the neutral and size it for 30 (unless you are firing a Sigma Arc) because when you load the 50, some of the load will be going out the other 50.

Don't bother running a ground unless your local inspector requires it.
Bury a new ground rod at the new service box.

Bury two plastic conduits. Put the service power in one and use to other for communications, like Cat6 or TV coax or ?? (Who know what is next - fiber maybe?) Do Not Use 90s. Split the turn between two 45s.

Think about burying a water line out there too.

Digging is cheap, unless you have to dig it up to do it again.

Do I have to add BTDT????

Matt
Matt & Mary Colie
A sailor, his bride and their black dogs (one dear dog is waiting for us at the bridge) going to see some dry places that have Geocaches in a coach made the year we married.

Cummins12V98
Explorer III
Explorer III
enblethen wrote:
You can use a different insulation on the wire that is less expensive if it goes in conduit as compared to USE type direct burial wire was my point.


Still needs to be rated for potential water that can get into conduit.

I thought I was being smart bu pulling romex thru 3/4โ€ pvc that was well glued. After a couple years the hot went to ground.
2015 RAM LongHorn 3500 Dually CrewCab 4X4 CUMMINS/AISIN RearAir 385HP/865TQ 4:10's
37,800# GCVWR "Towing Beast"

"HeavyWeight" B&W RVK3600

2016 MobileSuites 39TKSB3 highly "Elited" In the stable

2007.5 Mobile Suites 36 SB3 29,000# Combined SOLD

enblethen
Nomad
Nomad
You can use a different insulation on the wire that is less expensive if it goes in conduit as compared to USE type direct burial wire was my point.

Bud
USAF Retired
Pace Arrow


2003 Chev Ice Road Tracker

map40
Explorer
Explorer
Old-Biscuit wrote:
๐Ÿ™‚
enblethen wrote:
3% for voltage drop.
Hopefully, Old Biscuit is indicating copper wire and not aluminum.
Direct burial or are you going to put in conduit?



:S

I was going to have the GHana Dancing Pallbearers to do the burial ๐Ÿ™‚
Alfa SeeYa
Life rocks when your home rolls

Old-Biscuit
Explorer III
Explorer III
๐Ÿ™‚
enblethen wrote:
3% for voltage drop.
Hopefully, Old Biscuit is indicating copper wire and not aluminum.
Direct burial or are you going to put in conduit?



:S
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

garym114
Explorer II
Explorer II
Use the calculator at the bottom of this page. It gives you the voltage drop.
https://www.powerstream.com/Wire_Size.htm
2000 Sea Breeze F53 V10 - CR-V Toad
Some RV batteries live a long and useful life, some are murdered.
Get a Digital Multimeter and Learn How to Use It

MEXICOWANDERER
Explorer
Explorer
A pair of 600 volt transformers Major reduction in wire cost.

ktmrfs
Explorer
Explorer
naturist wrote:
I'll second what @Old-Biscuit said. Don't scrimp on wire. As wire is expensive in those sizes, it is none the less the cheapest part of the whole deal, when you consider also the just the hassle of blown fuses/breakers, brown-out damaged gear, etc.


x2. the other consideration for going for a 3% drop is the implications of any inductive load such as an AC motor, like your air conditioner. starting current for that could be 50-70A or so momentarily. with to small a wire size, voltage drop can be large enough to turn that momentary draw into many seconds, or even having the motor stall and not start due to voltage drop and if your lucky only pop the breaker.
2011 Keystone Outback 295RE
2004 14' bikehauler with full living quarters
2015.5 Denali 4x4 CC/SB Duramax/Allison
2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!

Gdetrailer
Explorer III
Explorer III
Old-Biscuit wrote:
3% Max Voltage drop for that 200' run

Otherwise you will have Low Voltage any time the supply voltage drops below 115V


50A #1AWG
30A #3AWG

Do NOT scrimp on the wire size...........


Agree with not scrimping on the wire but might get sticker shock when you get the prices for this..

#1 AWG copper single strand is going for around $1.90 per ft

For 50A 240/120 you will need 3 runs of #1 (two HOT and 1 Neutral) and 1 run of #3 (for ground)..

I suspect by the time you buy wire, conduit and other needed materials you will be north of $2,500 and if not doing the work trenching and installing conduit that labor cost could easily get you well above $3500..

I would suggest, finding a closer spot nearer to your electrical source that could knock off 100 ft of wire which would get your cost a bit more reasonable..

Alternately, nothing says you HAVE to breaker it for 50A, you could run 240/120 but use a lower amperage breaker like a 30A double instead of 50A double. That would allow you to use lighter ga wire..

ssthrd
Explorer
Explorer
map40 wrote:
Lynnmor wrote:
2oldman wrote:
advice.


Thank you for that, I cringe whenever I see this and it reminds me of the state of education in America.


No, no, don't go blaming the state of education in America. Here is the problem: I speak 6 languages and use them frequently, so my phone and computer do not know what I am writing and the autocorrect wants to commit suicide every time I chat with somebody different. You should see it when I go from Spanish to Cantonese...


That would be horrible...........

Old story about a Ferrari owner who had a mechanical problem, and couldn't decide whether he should consult a mechanic who just graduated from Ferrari School, or the old guy down the street who was "uneducated" but has been working on Ferraris for 30 years. Hmmmmmm....... Wonder what he did.

Sorry to get sidetracked. Couldn't resist.
2014 Keystone Laredo 292RL
2013 Palomino Maverick 2902
2018 GMC 3500HD, 4x4, 6.5' box, SRW, Denali, Duramax, Andersen
DeeBee, JayBee, and Jed the Black Lab

The hurrier I go the behinder I get. (Lewis Carroll)

map40
Explorer
Explorer
Lynnmor wrote:
2oldman wrote:
advice.


Thank you for that, I cringe whenever I see this and it reminds me of the state of education in America.


No, no, don't go blaming the state of education in America. Here is the problem: I speak 6 languages and use them frequently, so my phone and computer do not know what I am writing and the autocorrect wants to commit suicide every time I chat with somebody different. You should see it when I go from Spanish to Cantonese...
Alfa SeeYa
Life rocks when your home rolls

valhalla360
Nomad III
Nomad III
Google voltage drop calculator.
Tammy & Mike
Ford F250 V10
2021 Gray Wolf
Gemini Catamaran 34'
Full Time spliting time between boat and RV

time2roll
Nomad
Nomad
Yes 3% although for a dedicated RV you can probably size it for 35 to 40 amps but not less than #6.