Lantley wrote:sonicsix wrote:sdavis622 wrote:
Well, first I am no electrician! I saw this done on another forum, or by another member, can't recall. Basically I just figured it to be a hard mounted extension cord. Most electrical posts at campgrounds have breaker on the 20a plug so I figured that would cover it. Maybe I should add a GFCI... never thought about that! Thanks for the insight. Like I said I am no electrician, and this seemed simple enough.
I did this mod a while back, and I used 14 AWG wire. This outlet is used for a toaster oven, a griddle or a hair dryer. Always one at a time, so overloading the wire is not a worry. The cords on the appliances are much thinner than the 14 AWG wire I used to wire the outlet.
The issue has nothing to do with the cord on the appliance. The issue involves protection on the circuit. Sdavis22 installed 15 amp wire on a 20amp circuit. In the event of an overload the 20 amp breaker will not trip until 20 amps however the wire will begin to heat when the current exceeds its 15 amp rating. This heat has the potential to start a fire. 14 wire is designed to work on a 15 amp circuit not a 20 amp circuit. 12 wire is rated for a 20 amp circuit.
Keep in mind if your appliance has a short in its cord or anywhere else the circuit,the breaker is designed to trip. If the wire is not properly matched to the breaker the circuit may never trip. The wire will heat up just like it is part of the toaster. Only instead of toasting bread it may toast your RV. Using an underrated wire is just plain wrong and a potential hazard. All Romex wire is not created equal. They make different wire for different applications.
Sound advice and an easy fix.