DiploStrat wrote:HMS Beagle wrote:
It may be a little overboard, but I have considered adding the second alternator to the truck (an option on most 1T) but keep it off the truck electrical system, feeding only the camper house batteries through a good external 3 stage regulator. But in the sunny West, I find that 200W of solar on the roof is all that is every needed.
Some comments/observations, if I may.
-- I don't have a Ford shop manual, but I suspect that you will find that you already have a multistage regulator on your truck.
-- The "trick" to getting your truck's alternator to step up and do its share of the charging is to lower the resistance between your starter and camper batteries. Most RV's are wired with tiny 6AWG runs between the two batteries. (Worse, some also use diode isolators.) With a wire that small, you can drive all day and never really achieve a decent charge of your camper batteries.
-- You really need at least 50mm2 of copper (and a good ground) to make things start to happen. This means a minimum of 1/0 AWG cabling. I use a pair of 1/0 AWG cables, which comes out to 100mm2. Once you get the resistance low enough you will find that you start to get a significant bulk charge from your vehicle alternator, a charge that quickly (1 - 2 hours) gets you into the absorb stage where your solar controller can finish the job.
This voltage drop calculator is a nice tool. I have preloaded it with the following assumptions as a starting point:
-- 14v
-- 1/0 AWG
-- 100A alternator
-- 20 feet of cable from the alternator to the camper battery.
As you will see, the voltage drop is so such that you are actually starting to charge at a typical "float" voltage. That voltage will rise, however, as the amp flow decreases. (For giggles, reduce the wire size to 6AWG, a very common size, and the voltage drops to under 12.5v; essentially useless.)
Voltage Drop Calculator
Based on my experience, I would suggest that rather than spending money on a regulator to replace the one you already have, spend the money on good cabling, it will be expensive enough. If your camper is removable, you will have the additional cost of big Anderson Power Poles or similar detachable connectors.
Best wishes.
โMar-17-2016 06:17 AM
โMar-17-2016 05:49 AM
rwiegand wrote:
I wonder if using a pair of step-up/step down transformers would be a better solution than having to run such massive wires? I'g guess that the stock wiring would be quite adequate if you stepped the voltage up to 48 V or so. I'm no electrical engineer, but that seems to be the general solution to voltage drop in power transmission.
โMar-17-2016 05:46 AM
DiploStrat wrote:
GRRRR! Having trouble getting RV.net to take a post.
โMar-17-2016 05:45 AM
ticki2 wrote:
http://www.silveradosierra.com/electrical/voltage-fluctuate-on-the-dasboard-meter-t19680.html#p18011...
This may shed some light on the subject , at least as far as GM . Apparently my 02 is too old for this feature . t might also explain why some GM owners are having trouble charging coach batteries from the truck .
โMar-16-2016 04:27 PM
โMar-16-2016 03:56 PM
โMar-16-2016 02:29 PM
โMar-16-2016 02:27 PM
ticki2 wrote:
Can you verify that your trucks voltage regulator has three stage charging ?
โMar-16-2016 12:45 PM
billtex wrote:Fisher Bill wrote:
So we started out with a used setup that has two deep cycle batteries and a 1000W inverter in the Genny cabinet.
I have a 3500 propane generator and I strap it on a cargo rack and I haul another 7.5 gallons of propane if we think we're going to end up boon docking but really all we need is coffee (coffee maker) in the morning.
Wow...all that for a pot of coffee.
Our French press weighs maybe 1#...just sayin'
โMar-16-2016 11:43 AM
Fisher Bill wrote:
So we started out with a used setup that has two deep cycle batteries and a 1000W inverter in the Genny cabinet.
I have a 3500 propane generator and I strap it on a cargo rack and I haul another 7.5 gallons of propane if we think we're going to end up boon docking but really all we need is coffee (coffee maker) in the morning.
โMar-16-2016 11:35 AM
โMar-16-2016 09:15 AM
HMS Beagle wrote:
I haven't checked the new truck, the old one certainly did not have 3 stage charging. Regardless, having the start and house batteries connected directly means one or the other is not getting charged correctly, since they are unlikely to have the same State of Charge, or chemistry, or voltage.
With an isolated alternator/regulator and remote voltage sense, these problems go away and extra large cables aren't necessary. #8 or #6 is adequate to carry the current, and the voltage drops are accounted for.
โMar-16-2016 09:06 AM
DiploStrat wrote:
Some comments/observations, if I may.
.....
โMar-16-2016 08:42 AM
DiploStrat wrote:
Some comments/observations, if I may.
-- I don't have a Ford shop manual, but I suspect that you will find that you already have a multistage regulator on your truck.
Based on my experience, I would suggest that rather than spending money on a regulator to replace the one you already have, spend the money on good cabling, it will be expensive enough. If your camper is removable, you will have the additional cost of big Anderson Power Poles or similar detachable connectors.
Best wishes.