SoundGuy wrote:valhalla360 wrote:
The trick to running the air/con is it takes 2-3times the power to get the compressor turning. Once it's turning, it takes far less to keep it turning. That's why it looks like the 9-11amps the air/con is rated to draw should work but it really needs more like 20-30amps to get it going.SoundGuy wrote:
Repeated often but a misconception for sure ... initial compressor lockup current draw, referred to as Locked Rotor Amps (LRA), typically runs ~ 60 amps for a 13,500 BTU A/C. Sure, the time involved is brief, too quick for any DVM to see it, but it is real and it is what will task any 2K genset.valhalla360 wrote:
You are arguing technicalities when you basically said the same thing.
Of course we're debating technicalities, that's the whole point. :S A typical 13.5K BTU A/C does not draw just 20 to 30 amps on startup but in fact what is called it's LRA which is typically in the 60 amp range.Yes there are tricks to help such as getting the fan going first and you can put a capacitor in to help with the surge but any way you slice it that little 2000w unit is being pushed to the limits.
Exactly what I've always said BUT there's FAR more that one can do to help ensure success in starting a typical 13.5K BTU A/C with a 2000 watt genset, the first being to pick the right 2K genset as they're not all equal. IMO Honda's EU2000i holds the trump card here because it can successfully meet it's surge rating (and beyond in actual testing) for up to a half hour, far longer than any competing unit in this class. Yes, adding a hard start cap will in most cases also really help but simply starting just the fan first, then the compressor is the simpleton approach ... instead wire the thermostat with a fan switch that has a centre off position and one can then start just the A/C compressor, then add the fan load once the compressor has ramped up to speed and stabilized. Further, switching genset dino oil for a quality synth oil like Mobil 1 can really help a marginalized 2K genset meet that initial load demand much more easily, as I've clearly demonstrated to myself on multiple occasions with two different EU2000i gensets. Obviously, in any given situation there's not much one can do about the effects of elevation on a genset other than ensure it's running the appropriate main jet for that particular air density and not much one can do about increasing outside ambient temperatures that cause A/C head pressure to also increase and therefore increase starting load but regardless, the devil is in those details you call "technicalities" which often can be improved upon and will often spell the difference between failure and success. Been there. ๐
โMay-30-2015 05:31 AM
valhalla360 wrote:
The trick to running the air/con is it takes 2-3times the power to get the compressor turning. Once it's turning, it takes far less to keep it turning. That's why it looks like the 9-11amps the air/con is rated to draw should work but it really needs more like 20-30amps to get it going.
SoundGuy wrote:
Repeated often but a misconception for sure ... initial compressor lockup current draw, referred to as Locked Rotor Amps (LRA), typically runs ~ 60 amps for a 13,500 BTU A/C. Sure, the time involved is brief, too quick for any DVM to see it, but it is real and it is what will task any 2K genset.
valhalla360 wrote:
You are arguing technicalities when you basically said the same thing.
Yes there are tricks to help such as getting the fan going first and you can put a capacitor in to help with the surge but any way you slice it that little 2000w unit is being pushed to the limits.
โMay-29-2015 06:38 PM
โMay-29-2015 12:46 PM
valhalla360 wrote:
.....snip........
Yes there are tricks to help such as getting the fan going first and you can put a capacitor in to help with the surge but any way you slice it that little 2000w unit is being pushed to the limits.
โMay-29-2015 12:24 PM
โMay-29-2015 11:44 AM
โMay-29-2015 11:41 AM
SoundGuy wrote:valhalla360 wrote:
The trick to running the air/con is it takes 2-3times the power to get the compressor turning. Once it's turning, it takes far less to keep it turning. That's why it looks like the 9-11amps the air/con is rated to draw should work but it really needs more like 20-30amps to get it going.
Repeated often but a misconception for sure ... initial compressor lockup current draw, referred to as Locked Rotor Amps (LRA), typically runs ~ 60 amps for a 13,500 BTU A/C. Sure, the time involved is brief, too quick for any DVM to see it, but it is real and it is what will task any 2K genset. As for starting and powering such an A/C I have successfully and repeatedly done it with two different A/Cs, two different Honda EU2000i gensets BUT there are tricks to it. Anyone who wants to just plug in and have it work every time under all conditions should look for a larger capacity genset ... either that or replace the A/C with a lower draw unit of the same capacity - most manufacturers now offer them, including the new Atwood Air Command series which includes the 16K version the manufacturer calls "2000 watt generator friendly".