Jan 02, 2014Nomad III
Hi,
The continuous duty is 80% of 30 amps. i.e. you really only have 24 amps available for constant use.
The fridge draws more like 4 amps not ten.
For brief periods of time (read a second or two) drawing more than what the breaker is rated at will rather rarely trip it.
The continuous duty is 80% of 30 amps. i.e. you really only have 24 amps available for constant use.
The fridge draws more like 4 amps not ten.
For brief periods of time (read a second or two) drawing more than what the breaker is rated at will rather rarely trip it.