Hot water heater propane not igniting and staying kit

I posted here, because toyhaulers dry camp more often than hooking up and using the electrical side of our heater.

There is propane running through the line and out the flame tube. I have no ignition and shuts off after a few seconds. Any ideas would be greatly appreciated. The hot water heater is still under factory warranty.
  • donn0128 wrote:
    Suburban did have a bad batch of igniter boards a couple of years ago. But to effectively trouble shoot the OP must give is make and model number.


    We've had this unit since March '17
  • Suburban did have a bad batch of igniter boards a couple of years ago. But to effectively trouble shoot the OP must give us make and model number of his equipment.
  • Old-Biscuit wrote:
    So which BRAND/MODEL is IT :H


    Suburban I believe it's a D.E model

    I tried posting earlier, but the page kept asking if I were a bot.
  • D.E.Bishop wrote:
    I think there are only two possible problems, the igniter itself is bad or the igniter board is bad. The metal tip of the igniter should be about 1/8" from the burner and you should be able to see and hear it when the gas starts flowing. Excessive space and the spark won't jump the gap or maybe a loose connection from the board to the igniter.

    The board itself could be bad. There is a tester for the board and seeing as how it is under warranty, I'd take it to the dealer.

    Testing is a 30 second thing with replacement of BO parts a little longer.

    The procedure the heater will follow and trouble shooting instruction are probably in the manual.

    Shutting down after a few seconds of no ignition is a built in safety feature, same as the FAU heater.


    I've been reading the manual, there is no troubleshooting section.
  • What Brand/Model?

    If it is DSI (Direct Spark Ignition) then gas valve solenoid and Spark electrode are energized at same time.
    Spark electrode fires (Click, click, click) while gas flows to burner ---spark ignites flame and then 'flame proving' signal is sensed by circuit board and holds dc on gas valve/stops it to spark electrode.

    No spark....
    Wrong gap ----should be 1/8"--3/16"
    Bad wire connection from board to electrode...loose/dirty
    Bad wire thru ceramic...replace electrode
    Bad ground connection....electrode mounting screw provides ground....clean/tight
    Bad circuit board....spark circuit/high voltage transformer etc

    Water temp has to be down below 100*F/110*F (Brand/Model) in order for t-stat to close and call for heating. Otherwise no reason to heat.
  • I think there are only two possible problems, the igniter itself is bad or the igniter board is bad. The metal tip of the igniter should be about 1/8" from the burner and you should be able to see and hear it when the gas starts flowing. Excessive space and the spark won't jump the gap or maybe a loose connection from the board to the igniter.

    The board itself could be bad. There is a tester for the board and seeing as how it is under warranty, I'd take it to the dealer.

    Testing is a 30 second thing with replacement of BO parts a little longer.

    The procedure the heater will follow and trouble shooting instruction are probably in the manual.

    Shutting down after a few seconds of no ignition is a built in safety feature, same as the FAU heater.
  • nayther wrote:
    Do you hear the igniter clicking and see a spark? Can you light it with a match? The pilot lights first, then once it senses the heat from the pilot via the thermocouple the main burner opens and fires the heater.


    I can hear the igniter click and smell propane. I was able to light with a bic lighter. It shuts off after a few seconds. I only get it to flow the propane after I run water a few seconds, almost sensing low water to reheat again.
  • Do you hear the igniter clicking and see a spark? Can you light it with a match? The pilot lights first, then once it senses the heat from the pilot via the thermocouple the main burner opens and fires the heater.