homerbw wrote:
Sorry but I just have to ask. Realistically what would happen if I were to replace the 30 amp circuit breaker in the MH with a 35 or 40 amp breaker?
More than likely nothing. You would still be limited to 30 amps by the breaker at. The power pedestal. Now, if you were plugged into the 50 amp outlet with a dog bone 50/30 adaptor then you would risk the possibility of over loading the wiring between the power pedestal and the coach breaker box. The individual circuits would still be protected by the breaker for each circuit.