30 AMP breaker question

Sorry but I just have to ask. Realistically what would happen if I were to replace the 30 amp circuit breaker in the MH with a 35 or 40 amp breaker?
  • The wiring attached to the breaker would no longer be protected. The wire is probably #10 at 35 or 40 amp load, the wire would heat. Result probably a fire. Why do you want a 35 or 40 amp circuit?