Yes, I do it all the time. Worst case it will trip a breaker.
Sorry, Worst case is NOT tripping a breaker, but overloading the systems which results in HEAT buildup, which can lead to a FIRE. Your Post is a good example of the misconception of what a 120 breaker REALLY does. A Lot of bad things have happened to people that assume that the 120 breakers stop ALL bad results. I always ask customers, WHY do you think your 30 amp shore cord end is all burnt and pitted? Why is your 30 to 15 amp adapter slightly melted and burnt and pitted? WHY do you think your 50 to 30 Dogbone is Burnt and pitted on the 30 amp end? BECAUSE THEY OVERLOAD THE SYSTEM WHEN NOT CONNECTED TO 50 OR 30 AMP SERVICE. Doug
Ummmmmm and I always thought it was because the hardware wasn't up to snuff these days. I mean when I'm not pulling no more than a constant 15amps and a 20amp plug and outlet is cooking a good bit, like when running the rear air off of a separate circuit, then I'm gonna believe it's not built as heavy as it should be. Granted, it doesn't help having low voltage and maybe the circuit is pulling more than it should be.
Whatever the case, these 15amp plug and outlets need to be upgraded to better than 20amps as well, since they're used interchangeably so much and with 12 wire and 20amp breakers feeding 15amp outlets in most homes throughout America.
As for 30amp hardware, I changed out for a 50amp plug on my old 30amp coach and rid myself of this problem forever. Thing is, if you plug into a loose and burned outlet, it will ruin what you have and then when you plug into a good one, it will ruin it, creating a chain reaction, that never quits. Again, many of this 30amp equipment, isn't worth a darn, either and should be good for at least 40amps IMO. I guess we could blame it on the Chinese, like everything else, but then where is UL coming from, with all this?