oyly's avatar
oyly
Adding extra batteries
I've started looking into adding two extra batteries to my Winnebago Via 25P. This is to give myself enough battery power to make the furnace heater fan last through a night
My main concern with this is whether or not the power converter will cope with the extra capacity. Doubling the battery capacity should double the required charging current. The Winnebago web page says the converter is only 45 amps, which makes me worry it will not be sufficient to charge 4 group 24 batteries.
Doing some math with numbers from the power converter manual: In boost mode (14,4V), a 125Ah battery was returned to 90 percent charge from 0 percent in 8 hours. I currently have two batteries with unknown Ah rating, but reserve capacity of 140, so total Ah for both batteries should be around 140Ah. Assuming these will be returned to charge at the same rate as the 125 Ah battery, the charging current should be: 140*0,9/8 = 15,75 A.
Double that capacity, and I would need 31,5 A charging current, which leaves me with 45 - 31,5 = 13,5 A free to use during boost mode charging. This seems to me like I would normally be fine, and occasionally overload the converter, which should the shut down due to either the short circuit protection or the thermal protection.
