BTPO1 wrote:
I agree with what has been said above, but one thing has been left out. Once every thing has been cut out or disconnected you should always check for voltage on the device that you are working on. It only takes a fraction of a second to kill you if the right conditions exist. JMO
THANK YOU! You beat me to it....electricity can kill you!
Get a meter and check for any hot wires after you remove the panel off the breakers. The "Hot" leads coming INTO the main 50amp breaker will still be HOT with the breaker OFF if there is still power to the coach.
The larger coaches have THREE ways to get juice...shore power, inverter power from the batteries, and the generator. To be completely safe, the coach should be unplugged, the generator breaker disconnected AT the genset, and the batteries disconnected. IF you have an autoswitch, the genset could start while you're fiddling with the breaker panel. Err on the side of caution. Since you're not familiar with electricity I will say it once again:
1. Disconnect the coach from shore power.
2. Turn Genset OFF by switching OFF the breaker ON the genset.
3. Disconnect your batteries.
4. Check for live wires INSIDE the breaker panel AFTER removing the cover.
After all this is done, grasp the offending breaker at the front and wiggle it back and forth while pulling. It will swivel out. Reverse the procedure to put the new one in.....Dennis