pianotuna wrote:
Hi Lady Fitz,
Thanks for the link. I'll read it carefully.
22 amps @ 240 volts--but I believe (or I hope) it is balanced between the 2 120 volt "legs". So wattage is 5280 and btu's are 18016 giving a total daily maximum output with no voltage drop of 432384 btu's.
I see the 50 amp ones are balanced--but the biggest is only 21.6 amps
That means a few less watts and a few less btu's
21.6 @ 120 x 2 = 5184 watts = 17688 x 24 = 424512 btu's per day with zero voltage drop.
I'm not terribly familiar with voltage drop on 50 amp units. Is it an issue from time to time?
As long as the wiring is sized appropriately for the current draw and distance of the run, it won't be an issue. 10AWG usually would be plenty for even the largest unit (that is rated for 30A and only 22A is being drawn). It's not likely an RV will have a run from where the power enters the RV to the Cheap Heat that will be long enough for voltage drop to be an issue. Normally, a 60' run of 10AWG Romex will handle 30A at 240v with only a 2% voltage drop (roughly 5v). I can't see any installation using more than 10-15' from the power source which would keep voltage drop down to 2.4v or less, normally not enough to loose sleep over.
Keep in mind that this is assuming the supply source has been adequately wired. If the wiring to the pedestal is inadequate for the total load being placed on it, for example, then there will be an excessive voltage drop. Calculating voltage drop can be a real headache (and a pain elsewhere) because of all the variables that can be involved.