J-Rooster
Feb 05, 2018Explorer
Electrical?
I’m currently camping at the Palm Springs, Joshua Tree KOA. The power went out purposely today for 4 hours. There were workers, working on the underground power lines. My question is can I run my gen ...
DrewE wrote:
The transfer switch will prevent backfeed. It's designed and (UL) listed to perform that specific function. That is the primary safety requirement for a transfer switch--that the two sources never be connected to each other. They are designed so that, should they fail, it would be in a safe manner.
It's equally as bad to have the transfer switch connect the generator to the line when the line is live, as the two would almost always not be in phase with each other and the line would drive the generator and vice-versa, quite likely resulting in physical damage to the generator. There are stories of the rotors of the giant generators in power plants being ejected from the power plant building when they mistakenly get connected to the grid out of phase; the same could easily happen to an RV generator. (There could also be pretty bad things happening if the generator were not running at the time; the generator would act like an electric motor, and accelerate the mechanical parts of the generator to running speed mighty quickly, possibly breaking stuff.)
That said, there's nothing wrong with unplugging the cord either, and doing so is an absolute guarantee that you cannot backfeed the campground electrical system.