j-d wrote:
Did your tech replace the ATS? If so, did he give you an instruction sheet? Can you post Make/Model of your ATS?
Starting to sound like the ATS doesn't "see" that the genset is running.
Have you looked under the dinette, seen if it's the ATS, looked for loose wires?
Safety first! Unplug the shore tie and don't be running the genset while you poke around...
I have an Onan 4000 GenSet generator and MagneTek Power Plus 6300 A series, model 6332 Power Converter with battery charger. The power converter is the box under my dinette. Is the ATS built into this unit? The only other thing under my dinette seat is the heater.
I found the breaker switch on the side of the generator and toggled it (per j-d suggestion).
I tried starting the generator from the switch at the generator. I also tried starting the generator using the switch on the vent hood over the stove. I waited at least 60 seconds every time before trying the A/C. It never came on. I also noticed the clock on the microwave isn't on.
I tried pressing the start button on the vent hood while the generator was running (per ofdpos suggestion). No help.
Looking back, I vaguely remember starting the generator, then a few seconds later, hearing a click from under the dinette seat. I'm not hearing that click now. I'm thinking the ATS isn't switching over.