BillJ999
Apr 04, 2016Explorer
Tony,
Just a quick comment. Usually, in RVs, there is no neutral-to-ground bonding within the electrical panel. The neutral bus is floating, as seems to be the case in yours. However, in the picture, there seems to be a ground wire very close to the neutral bus. If it were me, I push on it a bit to move it away from there so it doesn't touch.
William
Just a quick comment. Usually, in RVs, there is no neutral-to-ground bonding within the electrical panel. The neutral bus is floating, as seems to be the case in yours. However, in the picture, there seems to be a ground wire very close to the neutral bus. If it were me, I push on it a bit to move it away from there so it doesn't touch.
William