dougrainer wrote:
I am NOT suggesting anything. I never stated anything about the wire gauge of the 30 amp shore cord. What I am stating is simple. I have worked on RV's for 38 years and NEVER has a lower amp draw been suggested for a 30 amp rated system in an RV. Remember, I am old enough to have worked on RV's for almost 20 years BEFORE 50 amp was even an option or available. I have seen numerous 30 amp ends pitted and melted and that was caused by using a 30 to 15 amp adapter. NOT really low voltage, but when you adapt down and most RV'ers are pretty ignorant about adapting down and the problems that causes, the voltage does drop and the AMP draw goes up and that generates HEAT. That causes the pitting and melting of the adapter and if on a regular 30 amp shore CG plug and you do indeed draw MORE than 30 amps, which a LOT of RV'ers do, will cause the melting and pitting on the 30 amp shore cord ends. I have customers(probably thousands over the years), come into my service center and the 50 to 30 adapter is pitted and melted on the 30 amp end and rarely will I find one not damaged from running MORE amps than 30 thru that adapter. A LOT of RV'ers think that if they overload the system the breakers will protect the system. THEY DO NOT. You must have knowledge and manage your amp draw when connected to 30 amp service or when connected with a 50 to 30 dogbone if you do NOT have a onboard EMS system. Doug
If a 30 amp breaker does not trip at a continuous load over 30 amps, then what is its purpose? Why is it RATED at 30 amps?
Are not these devices there to protect those who don't know or understand electrical loads?
Never mind. Here is a chart that shows circuit breaker trip time delay. Which would support your comment for up to 125 percent over load.
Trip Time Delay CurveAnd this formula also supports your comments.
Multiply the amps by the volts. In most circuits, this will be 20 x 120 = 2400 or 15 x 120 = 1800. The number resulting from this equation is the maximum wattage load you can place on the circuit before tripping the breaker.
Richard