Surge Guard w/ ? Power pedestal - how do you handle this?

We just had a Surge Guard 35550 hard wired into our 2017 Newmar Ventana motorhome.

I've heard that the unit can be quite picky about power supplies and will not allow power into the coach if there seems to be any issues at all with the power supply. Of course, this protection is the reason we had the unit installed.

But I'm wondering... can the unit be TOO picky?

What do you do if you go into a park, get a space, find the Surge Guard won't accept power and the park insists that their pedestal is fine and they can't offer you a different space?

Has this happened to any of you and how did you handle the situation?

I'm beginning to think that we would have been better off with a non-hard wired unit, that way we could easily bypass the surge guard in situations where we decided the risk would be worth removing the unit?

I'm considering having the 35550 re-wired with plugs to allow easy removal, if need be. Does this sound like a good move?

Looking forward to your thoughts and experiences with this kind of thing.

32 Replies

  • I always check the power pedestal BEFORE plugging my rig in - period. That said, I also trust the Surge Guard protection more so than most of the people I've seen that work on the pedestals in campground. I had to teach one of the techies in a Washington campground. Before hooking up, I notified them the pedestal was hooked up wrong. He questioned it and I showed him on my meters where it was wired wrong. He pulled the cover and sure enough, the wiring was not correct. Trust your surge protector....Dennis
  • Trust your Surge Guard.......

    CG 'electrician' might know just enough to be dangerous

    No other sites.....power pedestal questionable due to Surge Guard protection.
    Ask for refund and find another CG

    Unless you KNOW for sure that YOUR Surge Guard is broken then do NOT bypass it and plug in rig..$$$$ if Surge Guard right

    Feeling lucky---punk :B

    Can't leave.....RUN Generator as much as needed



    Personally I test any questionable power pedestal myself

    50A Receptacle
    L1 to Ground........120V AC
    L1 to Neutral.......120V AC

    L2 to Ground........120V AC
    L2 to Neutral.......120V AC

    L1 to L2------------240V AC

    Ground to Neutral....0V AC (ZERO)



    No 120V AC when testing L1 (L2) to Ground.
    Leave probe in Ground and place probe for 'Hot' into Neutral.
    Read 120V AC-----Reversed Polarity (Ground/Hot mis-wired)

    Big difference in readings.....HOTS to Neutral AND HOTS to Ground---short to ground

    Which do you want to trust..... CG 'electrician', Surge Guard/Yourself??